Yep...no worries. It'll probably only last 1/2 as long as a SS valve, so...5 years?
So, this is being fed with warm water? Have you noticed
soap suds in your rinse water tank? Does the rinse water tank overflow overnight?
If yes, then your entire water supply could be "contaminated" with
soap/wax. That's because a leaking check valve sends high pressure water backwards into the facility plumbing...maybe all the way thru the softener(s) and boiler. About the only thing that stops the backwards flow is the backflow prevention device at the service entrance. This only happens when that particular bay (with the faulty check valve) is used in the
soap/rinse/wax selections.
I've always found it to be good practice to use low pressure poly tubing from the weep solenoid to the check valve. This makes a mess when a check valve fails because the poly tubing will burst. But, at least you know you have a problem because the bay will be frozen and there will be weep water spraying all over the engine room.