I operate a 5 bay wash it uses the dixmor led7 timers they only last maby 6-8 months and die. I have a whole box of dead ones. Is there anyone who fixes them?
 

Fatboy769

Living the American Dream
Joined
Sep 4, 2007
Messages
423
Reaction score
83
Points
28
I operate a 5 bay wash it uses the dixmor led7 timers they only last maby 6-8 months and die. I have a whole box of dead ones. Is there anyone who fixes them?
Maybe Dixmor? What exactly is happening to the timers? I’ve had very good luck with the LED 7 timers.
 

TMoliver

Active member
Joined
Apr 28, 2023
Messages
112
Reaction score
71
Points
28
I do not use the Dixmor timer but you should be seeing 6-8 + years out of them. First is check your voltage in ever meter box with nothing running in any bay it should be between 23-28 VAC. Next turn on several bays at one time select the same function in each bay check voltage again. it should not drop much make sure you check on all functions especially low pressure if you are using multi plexer like MX8 or MX10 to operate that pump. if your transformers are not in phase you will see voltage increases anywhere from 1.5 times to almost triple.

Just some where to look for the issue.
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,717
Reaction score
2,027
Points
113
We use a lot of Dixmor LED-7 timers. We have very few problems with them. Yes they are repairable, normally it costs around $45-$55 to have one repaired. I had a customer who was having LED-7 timer issues, his load was to high for the timer, the timer is only rated at about 3-5amps. He ended up installing a relay so that the only thing the timer was controlling was the relay, no more problems. If you also have a problem with someone beating on the front of the coin box, that will damage the timer.
 

Al fittn

New member
Joined
Jun 28, 2024
Messages
2
Reaction score
0
Points
1
Yes we had a car/truck accident that snapped a pole and the 13k touched the low volt lines under them and ruined all of the electronics card readers and every motor that was running at the time. All 3 ph stuff but that was last year. I haven’t checked running voltage yet. But I certainly will. Thanks for the feedback. Al
 

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,808
Reaction score
423
Points
83
Location
Ohio
I have Led 7's that are over 20 years old and don't think I've ever had one fail. Like others have suggested, don't overload the timer and check voltage in the ER AND inside the meter box to make sure its in the right range and you are not getting voltage drops.
 

edredtop

Well-known member
Joined
May 28, 2009
Messages
243
Reaction score
270
Points
63
Location
California
Yes we had a car/truck accident that snapped a pole and the 13k touched the low volt lines under them and ruined all of the electronics card readers and every motor that was running at the time. All 3 ph stuff but that was last year. I haven’t checked running voltage yet. But I certainly will. Thanks for the feedback. Al
LED 7s have been workhorses, the only ones that have gone bad for me is when the load wire finds ground in the coin box. (2 in 20 years)
To Randy's point about unwanted abuse to the timers, I've had great success using a spring with the fasteners to absorb the shock of a hit (see attached). Not pictured is a small flat washer to go between the timer and the spring. It's also one of several reasons to use tip protectors on the wands too.
 