Boiler gets wet everytime it rains!

partonken

New member
Joined
Apr 1, 2014
Messages
19
Reaction score
0
Points
1
Location
stayner ontario
I have a boiler with a vent pipe going straight up out the roof. Every time it rains I get water on the boiler and worse inside the boiler. I have tarred the edges around the flanges on the roof and the whole assembly looks water tight. There is a skirt that goes around the main vent , im wondering if I should use a high temp sealant to seal it. if you look from in the rafters you can see light through this round crack. Any ideas. thanks
 

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,322
Reaction score
808
Points
113
Location
Leominster, MA
Is this a 80%eff boiler with metal pipe or high efficient boiler with pvc vent pipe? Ether way to sounds like you may be missing a storm collar.
 

partonken

New member
Joined
Apr 1, 2014
Messages
19
Reaction score
0
Points
1
Location
stayner ontario
its a weil and mclain , not high efficiency. Its a steel pipe approx. 12" diameter then when it goes through the roof it goes down to an approx. 8" diameter surrounded by a storm collar. Im wondering if I should high temp seal the seam were the storm collar meets the main pipe??
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,949
Points
113
Location
Texas
As a rule you shouldn't rely on sealant to keep water out of a roof penetration. Is there a rubber boot around the vent pipe that's sealed to the roof?
 