Second time our 25hp overload has tripped and I cant find anything wrong, has anyone has a problem with the heat we have had this year?
 
Joined
Nov 9, 2007
Messages
330
Reaction score
1
Points
16
Location
CT.
Have you checked all 3 legs with an amp meter? If so the the overload may be geting weak. Have you checked the wires on the top and bottom to make sure they are not loose, also check the contacts to make sure they look good.
 

ken-pro

Equipment Distributor
Joined
Aug 31, 2007
Messages
140
Reaction score
2
Points
16
Location
Kitchener, Ontario
Shut off the power, then check all wire connections between the breaker panel and the motor starter. Then check all connections between starter and motor.

On more than one occasion I have seen a loose wire connection cause motor overload tripping - Especially on larger motors, and where vibration might be a factor.

Also, double check the adjustment for the overload. It should be set a little higher than the full load amps for the motor.

Check the amperage draw while running full pressure - A partially plugged nozzle combined with a regulator set too high can cause increased running amperage.
 