Quick question guys, can I run two separate switching wires from a honeywell thermostat if they are not operating on the same 24 volt system? My gut instinct tells me no, but I figured I might as well check.

Thanks in advance
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
Yes, if the 24V transformers are on the same 120V leg or 240V pair. The easiest way to tell would be to put a voltmeter across both 24V "hot" sides, and the voltage should read zero. If one is supplied 120V and one is 240V it won't work - you might get 48V to one switched device.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
I see. So if both of the 24 volt transformers are fed the same primary voltage, then I will be okay?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
It should be; it's worth checking to be safe.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
I ended up getting 50 volts which is why I'm just going to install a second thermostat. Just to clarify, I don't want there to be a signal if the temp is above the setpoint so I should set it up as a "close on rise of temperature" correct?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
No, "close on rise" closes the circuit and sends power when the temp is above the setpoint.

For about $10 you could add a micro DPDT relay to split the switch for two circuits.
 