cantbreak80

Maybe I need new clubs
Service call to restore a troublesome 5 year old Lochinvar Armor.
Site Manager stated “Maintenance required” has been displayed since he’s been employed.
Difficulty accessing User Interface…wonky display. Finally got the Fault screen to display ”Flame Sense” (10 times).
Quite apparent that the boiler has never been serviced.

Took it apart…
• cleaned combustion chamber and burner
• replaced ignitor, flame sensor and User Interface Control board.
• Performed combustion analysis and adjusted for proper CO/CO2.
Back in service. Happy customer.

FWIW…ModCon boilers are quite efficient but require regular service, especially if they’re in high volume locations and even more so when improperly commissioned/set-up.