Pump Drive Fault

Flex- Wand

Member
Joined
Jun 13, 2020
Messages
100
Reaction score
19
Points
18
This is a 2 arm saber, first fault pump drive, reset then shorty after pump drive fault an drive com fault. So I opened the MCC panel the pump drive F700 smell burnt . So do I start testing the pump motor wires ? Something got hot ? Very thankful for your Support.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
It will do that if it gets hot. It wouldn't hurt to leave the cabinet open with a fan blowing in it. Also make sure the pressure isn't getting too high.
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
Belanger didn't design the vfd cabinets right on the saber, that's for sure. Way too small nema 4x cabinet sealed with no ventilation and running 4 drives. Check the drive and see if it says fn. That is a fan error which tries to keep it cool. I have piped in conduit on the sides high and low with turn down elbows to keep water from coming in, then powered air through the cabinet with fans that mounted to the 3 inch conduit. If you have the fan error, you need to replace the integrated fan for the drive. But it may be too late...
 

Flex- Wand

Member
Joined
Jun 13, 2020
Messages
100
Reaction score
19
Points
18
Pressure or pump speed ? Thank you both the VFD reads E.Uur an will not reset . That's a good idea for the hole an down tube. I mentioned cutting holes to the installer 7 years a go he just look funny at me. I thinks it's toast. I lost a carriage drive on this bay years before a wire in the bay rubbed though. Burned it out when I reset it.
 