Spot Free Pump Short Cycling during Foam Brush

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
I am not sure how long this has been going on, but I just noticed it this morning while I was up here at the wash. When a customer in bay 3 was using the foam brush, my distribution pump was running in roughly 15 second cycles shutting off for 1 or 2 seconds and then firing back up for another 15 seconds. This lasted the entire time the foam brush was being used and then stopped when the customer switched to rinse. So far as I could tell, there wasn't any voltage going to any of the bay solenoids so it appears as though it was just deadheading against the solenoid band. I just checked 2 of the other bays and everything was operating fine :confused:

Any ideas where I should start troubleshooting?
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Maybe a short between the foam brush and spot free? But wouldn't that cause the spot free solenoid to energize?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
Bubbles Galore said:
Maybe a short between the foam brush and spot free? But wouldn't that cause the spot free solenoid to energize?
Yeah, it would.

Someone had a similar problem recently, and I suggested moving that bay's wires to a spare input on the RO motor controller. He never reported back.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
So you're saying to disconnect the wires from the bay controller to the spot free controller and see if that is how I can isolate the problem to some type of short in the rotary switch?
 
Etowah

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Ok...I did a little more troubleshooting, but I am still not sure what to do...

- I tested the spot free and it was working fine. 24 v at the controller and all is well...
- I left the input wires connected to the spot free controller and turned on the foam brush...voltage read about 1.6 v...not much...but the spot free pump was running...
- I disconnected the input wires from the spot free controller and the spot free pump did not turn on when the foam brush was selected...would that mean that I am shorted out somewhere at the rotary switch? Meterbox? Bay Controller?
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
MEP - I read that post you were referencing and I am also running that same controller that Ric is using...the GS-16D...
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Any ideas?

When I remove the common from the spot free controller, the pump turns off...only the common though...thoughts?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
I would start by making sure your 24V hot and commons on all bays are in phase. Connect your volt meter to bay 1 24V hot and bay 2 24V hot, and there should be no voltage; same with the common. You should get the same reading on all bays as you move down the pump stands.

It could also be the "logic controller" in the pumpstand.

Do you have an extra set of inputs on the pump controller you can try?
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
That is going to be my next move is to switch to a different set of inputs on the controller and see where that leads me.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Moved the input lines from the bay controller to an open spot on the spot free controller with the same results...

Can I just jumper one of the commons from a different bay on the spot free controller? Will that work?
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Does anyone have any ideas as to how I can band-aid this thing? I have a couple days of sun coming and I really don't want to have this bay down...I'm open to any suggestions...I will do a little dance if it will help! :)
 

Bill Manke

Member
Joined
Aug 30, 2007
Messages
191
Reaction score
1
Points
18
Location
Reno Nv
do you have a rotary switch out in the bay? If so it sounds like it is making the connection out there. Try a new switch our swap from another bay and see what happens.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
It is an Etowah Valley Door and it is a 10 button rotary. The door is just about 6 months old and has worked fine up until this point...sadly, I don't have any spare rotary switches on hand...only when the sun is shining...
 

Bill Manke

Member
Joined
Aug 30, 2007
Messages
191
Reaction score
1
Points
18
Location
Reno Nv
How about all the connections to the rotary switch all the way back to your equipment room. check to see if you have any stray wires making a connection. Such as when you make your connections and twist the wires to put in connectors. Make sure now loose stands are touching the wrong connector.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
Bill Manke said:
How about all the connections to the rotary switch all the way back to your equipment room.
It's not the switch or the wiring anywhere between the bay and the room, otherwise the solenoid would open too. It's not a stray connection making contact otherwise two bays would run when one is called for.

Bubbles Galore said:
Can I just jumper one of the commons from a different bay on the spot free controller? Will that work?
If all your commons from the bays are interconnected somewhere, then that may work. It's worth a try, shouldn't take long to find out.

Did you ever check the phases of the voltage for all the bays?
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
It's not the switch or the wiring anywhere between the bay and the room, otherwise the solenoid would open too.
I was hoping it was that, but you are correct, there is zero voltage going to any of the solenoids when the foam brush is being used and the distribution pump is running.

If all your commons from the bays are interconnected somewhere, then that may work. It's worth a try, shouldn't take long to find out.
I tried this and it did not work...

Did you ever check the phases of the voltage for all the bays?
The voltage that feeds my bay controller(s) are daisy chained together from a 1.5 VA transformer, so theoretically shouldn't all the phasing equal out? I don't know, that's why I'm asking. For each bay controller the 24v comes into a separate ginsan controller and is distributed out to the terminal strips from there.

I am thoroughly confused seeing as how no matter where I place my input wires from my bay on the GS-16, the problem still persists, yet there isn't any voltage coming from the bay through the input wires. Yet, when I remove the common, the pump turns off...am I missing something?

I have asked Dan at Ginsan to give me a call this morning to see if he is familiar with this type of problem with the GS-16 controller...
 

Dan kamsickas

GinSan Technician
Joined
Aug 31, 2007
Messages
704
Reaction score
935
Points
93
Location
Grand Rapids, MI
John

Left you a voicemail.

One thing you can check: Measure across different inputs, for example the hot of 1 to the common of 2. If you read 24v anywhere on the 16D this way you are getting feedback from a short somewhere. It could be causing enough leakage current to trigger the input of the 16D but not enough to open the solenoid. I saw this once when someone did a jackleg job of installing a coin vac system. I suppose it could possible be caused by a bad rotary switch not totally breaking contact when it is turned.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
Bubbles Galore said:
The voltage that feeds my bay controller(s) are daisy chained together from a 1.5 VA transformer, so theoretically shouldn't all the phasing equal out?
It's supposed to, but I've seen all sorts of weird problems occur if the 24V transformers aren't in phase. It's easy to check and correct, and seems like a probable culprit since it's happening on only one bay that has had something changed.

Try just swapping the hot and common to the door.
 