This is a good head scratcher

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
792
Points
113
Got a call from a customer with an old self serve, no automatic. Lack of water coming out to the tanks. When one of my techs went there, he says, you pull down on the float in the main water tank, and mostly air comes out. Same thing with a hose bib on the wall. He thinks the water company is doing pressure tests. No, I tell him, turn off the main valve at the air compressor, and see what happens. It goes away. When the air is turned back on, everything is normal. There is no blowdown of any waterline at the place. This is FL and it doesn't freeze this far south. I'm going over there later to see if I can find a path, but can anyone suggest something? Just when you think you know it all.....
 

whitescout

Banned
Joined
Apr 2, 2008
Messages
177
Reaction score
3
Points
18
Location
Minnesota
Without knowing anything about your system, the first thing that pops into my head are multiple bad check valves if you inject air into your low pressure manifolds.
 

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
792
Points
113
Air is mixed with the low pressure chemicals at the manifolds over each bay. I have seen this air backfeed through the pump and into the tank. In this case however, the air was in the water line feeding the tank. Even the hose bibs on the water line before any equipment.
 

PaulLovesJamie

rural 5 bay SS
Joined
Aug 30, 2007
Messages
1,321
Reaction score
229
Points
63
Location
Kutztown PA
I cant think of any reason why turning the compressor off would have "solved" this - can you clue me in to why you even thought of that?

I cant really think of a solution, but my first thought is that I dont trust the water dept. They've changed my water pressure (by a lot) without telling me, turned the water off without telling me, etc.

I have pressure gauges all over the place - one where the water enters the building, one after the backflow preventer, one after the softener ... you get the idea. It's a cheap way to check my wash, a sweeping glance at 20 gauges every time I enter the equip room tells me a lot.

Anyway I guess I"m trying to say I'd put a pressure gauge on the incoming water supply, and I'd call the water co and ask what they were doing.
 

Wally

Member
Joined
Sep 9, 2007
Messages
176
Reaction score
0
Points
16
Location
Buford, GA
Mac my guess is it`s somewhere in the low pressure system, foam brush, tire cleaner.Somehow air is getting back into the hoe bib.
 

jprb

Member
Joined
Aug 31, 2007
Messages
312
Reaction score
11
Points
18
Location
Southeast Missouri
You said it's not in a freeze zone, but is there provisions for a weep system that might be hooked directly into the water line?

JPRB
 

robtl

central Ky
Joined
Sep 2, 2007
Messages
203
Reaction score
1
Points
16
Location
central Ky
Did you check where your backflow preventer was to see if it has dumped, maybe the water co lost pressure and air got into the system then.
 

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
792
Points
113
I had the tech turn off the air at the compressor because air was coming out of the water lines. It was just a hunch, and it may have been one of those odd coincidences that it stopped right then. There is a building right next door and its water was fine. Water dept said no work going on in the area. There is no provision for any weep system. This is an old place that has had a string of inept people working on it. It is leased from the owner and the lesee doesn't want to put any money into improvements, even gauges. Maybe UFOs were there doing something. If we find it, I'll let you know.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
If they were that inept, it's possible someone connected air straight to the water plumbing somewhere. I've seen dumber things done.
 

robtl

central Ky
Joined
Sep 2, 2007
Messages
203
Reaction score
1
Points
16
Location
central Ky
I once saw a automatic coffee maker tied into the sprinkler system in a office building,

go figure
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
robtl said:
I once saw a automatic coffee maker tied into the sprinkler system in a office building,

go figure
Was it so the sprinklers coming on would start the coffee brewing in the morning?

One of the dumbest things I've ever seen anyone do was at an old place of work, a girl at the front desk had a space heater plugged into the same power strip as the computer. It kept tripping the breaker in the power strip, so she unplugged the strip from the wall and plugged the heater in there. She plugged the power strip into the first outlet she saw: in the power strip, then called me in to see why her computer wouldn't turn back on.
 

pitzerwm

Active member
Joined
Aug 28, 2007
Messages
3,693
Reaction score
10
Points
36
Location
Tri-Cities, WA
When I worked for Singer Business Machines in 1970, we charged a number of people $75 to plug their unit back in.
 

bneckrock

Bill Neckrock
Joined
Sep 1, 2007
Messages
73
Reaction score
0
Points
6
Location
Detroit Suburbs
When I worked for Singer Business Machines in 1970, we charged a number of people $75 to plug their unit back in.
Bill, the mention of those old calculators brought back some memories of my first job in public accounting. The juniors used to set Fridens chunking along and sleep off a tough night. I wonder what happened to all those machines.
 

pitzerwm

Active member
Joined
Aug 28, 2007
Messages
3,693
Reaction score
10
Points
36
Location
Tri-Cities, WA
Fortunately, I came in just when the new electronic ones came out. It was no wonder they went under. We would get a box of 12 electronics from Japan and they all worked and lasted forever, we would get a box of 12 from the Singer factory in CA and 10 wouldn't work out of the box. I started moonlighting in my own business and the boss got mad and canned me, later they were all out of a job too.
 

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
792
Points
113
Mystery solved ! This was one of the strangest ones I've seen in a while. Here is what was happening. When some of the bays were on a foaming low pressure function, some of the foaming product went back through the high pressure hose to the pump. This is easier to do if you have non weep guns and someone leaves a bay on and drives off. This place has a weep system that is very old. The foaming product was going backward through the weep and into the main water supply. The product was about 50 psi, while the incoming water is less than that. So big soapy air bubbles would accumulate in the water line and burp into the main water holding tank. It would also back directly into the tank through the faulty main check valve.
 