Hey guys, I’m going to be replacing the timer on my vacuum as it appears to have lost its programming, as when a coin or token triggers the coin switch, it just pulses the contactor And does not start timing The timer is original to the vacuum and considering it’s about 24 years old, At least the actual timer Well the vacuum was made in about 2003, The only caveat about the original timer is The vacuum has a emergency stop button, so I would need to try and find a timer with a cancel function that I can attach the leads to the emergency stop button Or when power is cut to The timer that it Cancels the credit applied on the timer this is mainly a European thing, but not all manufacturers use it
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
Do you really need the cancel button?

What timer do you have now?
 
Joined
Sep 22, 2022
Messages
92
Reaction score
17
Points
8
Do you really need the cancel button?

What timer do you have now?


Sorry I didn’t get back to you, at the moment It currently has the original timer, And I found out what the issue is, after testing the timer and the motor starter separately, both seem to work fine separately, but I have noticed that when you have the timer connected to the motor starter it seems like the 24v Supply Voltage dips enough to reset the timer And so prevents the timer from starting its cycle ,I’ll potentially try putting the 24 V Transformer closer to The input supply Or potentially putting it on a nearby supply, as at the moment it is on the energized side of the contactor right next to where the motor starting current could potentially drop the voltage enough for just a second that through the 24 V transformer, the timer would lose voltage And reset [in the same fashion house sometimes a motor starting can make And reset [in the same fashion house sometimes a motor starting can make some lights dim
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
The transformer is most likely going bad. You would need a couple hundred feet of very small gauge wire on the low voltage side to cause a voltage drop.
 
Joined
Sep 22, 2022
Messages
92
Reaction score
17
Points
8
ahhhh Okay, It appears to be putting out 24 V when the motor is not connected, but when it tries to start it looks like it’s dropping And probably quite significantly, I’ll have a bit more of a look at it later on Tuesday
 