Weepmizer

washregal

Member
This I am sure is an odd question to many.. but here it goes. my upper limit on my dixmore is set to 114 deg.

I was at my wash earlier today and noticed 80 deg on the unit... and input 1 on... weep water was running.

When adjusting LL and UL

Does LL turn on the unit and UL turn off the unit? So say the UL should be set for say 36 deg F and the LL should be at 34 or 33?
 
Here are the programming instructions for the Weepmizer. You’re looking at the wrong section to program the Weepmizer.

www.dixmor.com/TIMER PDF/DX1000 INSTR.pdf

Here’s the trouble shooting information

www.dixmor.com/TIMER PDF/WEEP_TROUBLESHOOTING.pdf

To check the Low Temperature Push the “A” button once and “Log” will come up, push the “B” button and the “Lo temp” will be displayed.

Push the “A” button again and the “Hi Temp” will be displayed

To clear the “Hi” and “Lo” temps push the “A” button 5 times until the display reads “CLR” push and hold the “B”

The display will show “SURE” and then “DONE”


Raise or lower Temperature setting

To raise, lower or check temperature settings. Push the “A” button until you come “Prog”. Push the “B” button to check the ON temperature. To lower the on temperature push and hold the “B” button. To raise the on temperature push the “B” button one time. If no buttons are pushed in a 20-25 second period the weepmizer will go back to the normal operating mode.
 
You may want to call Dixmor. One of my units kept doing the same thing once the temperature got to be about 60F out. I would get back to the site and the weep is running continuously until I toggled the input on/off. Dixmor said there is a 'bug' in the program in the software version my unit is running.
 