I have an elevated RO tank and was experiencing dribbling wands, even after replacing all of the solenoid valves on the delivery pump. For a siphon break, I T'd this check valve into the line going to the bay
https://www.kleen-ritecorp.com/p-1733-kleen-rite-maxi-flow-check-valve-5000psi-14fxf-ss-hp.aspx
It seemed to work well enough until it came time for the weep system. My weep pressure is adequate for weeping, but not strong enough to make the valve "Check", so I get some dribbling. A new valve does the same thing.
Obviously, I'm using the wrong valve for this application, but don't really know what to get. Any suggestions?