aca carwash 2
Member
Before I get called out again, I called an electrician and paid $250 and compressor still not working.
3 phase
Compressor was running all the time and kicking breaker, pressure switch was leaking. replaced the pressure
switch before I realized the check valve was bad,replaced the check valve and the pressure switch with one that's not adjustable.
in other words could not adjust the variable of on/off cycling. the previous one was adjustable. the new one cycles from about 100-107
psi.
the breaker was still kicking 3/4 times a day. replaced the breaker. Didn't kick for a month, now kicking 3/4 times a day again.
trying to find out if its the contactor or need another pressure switch that cycles less around 110-150 psi, how can I test the contactor? Do you think its the pressure switch? coming on 5/10 times an hour.
Happy Thanksgiving!!!!!
3 phase
Compressor was running all the time and kicking breaker, pressure switch was leaking. replaced the pressure
switch before I realized the check valve was bad,replaced the check valve and the pressure switch with one that's not adjustable.
in other words could not adjust the variable of on/off cycling. the previous one was adjustable. the new one cycles from about 100-107
psi.
the breaker was still kicking 3/4 times a day. replaced the breaker. Didn't kick for a month, now kicking 3/4 times a day again.
trying to find out if its the contactor or need another pressure switch that cycles less around 110-150 psi, how can I test the contactor? Do you think its the pressure switch? coming on 5/10 times an hour.