6t7gto
Member
As the title states...what temp do you have your floor heat boiler set at?
I had my Raypak 514k btu set on #4. Manual says it is approximately 155*.
My boiler has sooted up on me and I need to clean it.
I lowered the setting to #3 (145* according to the manual) and it went down to 16* Friday night with a pretty good snowfall.
The floors are clear and dry.
I have a switch on my boiler to control the circulating pump either manual or automatic.
When it is forecasting low temps I switch the pump to manual.
When my system was originally installed a slab sensor was used.
We got poor results. So the contractor installed the slab sensor in the return manifold.
We use the stat for that sensor as a reference point of the return glycol.
Presently have this stat set to 65* to turn the burner on and off.
Thx
David