I have a wash that doesn't have three phase power, instead it has a phase converter to supply the automatic. This has worked for four other automatics in the past. My issue with it is the wildly different electrical readings on the three phase motors. There is 240 single phase going into the converter. I get quite different readings coming out. As a result when I read the amp draw on the 10 hp blower motors, I get 14 amps on one leg, around 24 on another, and around 35 on the last one. This is the same on all three motors. Anyone know of a way to get these more balanced out? The tech people for the converter say to install a buck and boost transformer before the converter. The data plate on the motors say it should only draw around 22 amps at full load current. Any ideas on how to get these more inline?