Self Serve - Breaker in control box getting stuck

Nknjeim

New member
Joined
Jan 23, 2021
Messages
23
Reaction score
1
Points
3
I got a self serve carwash, one of the breaker in the control box get stuck so often for hours... I have a cat pump 5CP2120W.
Is the problem with the pump or the breaker?
Thanks
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
I think you mean the contactor - the relay that puts power to the motor. Is that what you are talking about? A breaker will 'trip' and turn off power to the motor, but it will stay that way until it gets manually reset. They don't "get stuck". A stuck contactor means your contactor is either defective, or you possibly have a short circuit downstream that is causing the contacts in the the contactor to weld to eachother - effectively making the contactor stuck. But in that case, you would trip a breaker soon after turning it on.
 

Nknjeim

New member
Joined
Jan 23, 2021
Messages
23
Reaction score
1
Points
3
I think you mean the contactor - the relay that puts power to the motor. Is that what you are talking about? A breaker will 'trip' and turn off power to the motor, but it will stay that way until it gets manually reset. They don't "get stuck". A stuck contactor means your contactor is either defective, or you possibly have a short circuit downstream that is causing the contacts in the the contactor to weld to eachother - effectively making the contactor stuck. But in that case, you would trip a breaker soon after turning it on.
Yes it's the contactor (sorry)
It happens once (maybe) every 10 uses. I think as you said I have a bad contactor, otherwise, it won't work for not even once if I have a short circuit downstream, and also the breaker would trip too.
 

mjwalsh

6 bay SS w/laundromat
Joined
Sep 7, 2007
Messages
3,134
Reaction score
173
Points
63
Location
North Dakota
Yes it's the contactor (sorry)
It happens once (maybe) every 10 uses. I think as you said I have a bad contactor, otherwise, it won't work for not even once if I have a short circuit downstream, and also the breaker would trip too.
Based on our first hand experience ... your contactor possibly was undersized. In other words the amp rating for the contacts was too low for your equipment. Yes ... manufacturers have been known to undersize the needed amp rating so it is not always an operator or a former owner!
 

Nknjeim

New member
Joined
Jan 23, 2021
Messages
23
Reaction score
1
Points
3
Probably so, even though this carwash has the same contractor since it was built in 1997.
The problem is only in one bay, that started couple of weeks ago, and all others are working fine.
I will replace this contactor and see what happens.
Thanks
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
I got a self serve carwash, one of the breaker in the control box get stuck so often for hours... I have a cat pump 5CP2120W.
Is the problem with the pump or the breaker?
Thanks
What exactly is "stuck?" Does the motor stay running after time runs out? Or does the bay not work and after a few hours starts to work again? If it's the latter, it's probably the thermal overload tripping, taking some time to cool down and resetting automatically, assuming it's set to do so.

It's not going to be an undersized contactor or it wouldn't have worked for the last 23 years.
 
Last edited:

Nknjeim

New member
Joined
Jan 23, 2021
Messages
23
Reaction score
1
Points
3
Yes the motor stays running after the time runs out; I have to recycle the breaker in order to reset the contractor.
 

PrecisionPyro

Member
Joined
Dec 3, 2020
Messages
42
Reaction score
39
Points
18
Location
West Michigan
Yes the motor stays running after the time runs out; I have to recycle the breaker in order to reset the contractor.
I would never advise anyone to work on electricity while it's active, however if it were me, I'd check to see if the contactor has 24vac on the coil side while it's running, when is not supposed to. You'll rule out any sort of other issues (timer-panel) ETC, is there is no voltage there while running. Again, I would not recommend anyone do that unless properly equipped and trained... But that's what I would check first. Simple free test before replacing parts.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
Also look at the contactor, there's a bar in the center that you can push in to manually close the contacts and run the motor. If the one giving you problems doesn't look like it's coming all the way out like the others, one of the contacts is fused closed, which means it needs to be replaced.
 

Nknjeim

New member
Joined
Jan 23, 2021
Messages
23
Reaction score
1
Points
3
Also look at the contactor, there's a bar in the center that you can push in to manually close the contacts and run the motor. If the one giving you problems doesn't look like it's coming all the way out like the others, one of the contacts is fused closed, which means it needs to be replaced.
Yes this bar is stuck and not coming out, even if I try to pull it out, it doesn’t come out and keeps the motor running, until I recycle the breaker.
Thanks
 
Etowah

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
Based on this latest info, you need to trace down a control wiring or component problem. Something is likely powering the contactor coil if turning the breaker off makes it release. You need to check for control voltage when it's stuck on like mentioned above. If you have full control voltage there, you need to trace it back to the culprit. If your equipment is 23 years old, it's probably operated by a rotary switch. I'm assuming changing the rotary switch position doesn't release the contactor when it's stuck...? Might be helpful to post equipment type and if you have credit cards or manual override controls. Still could be the contactor though. Another assumption - no other work has recently been done, right? If some work was recently done, that could help narrow down the cause as well.
 

Nknjeim

New member
Joined
Jan 23, 2021
Messages
23
Reaction score
1
Points
3
Based on this latest info, you need to trace down a control wiring or component problem. Something is likely powering the contactor coil if turning the breaker off makes it release. You need to check for control voltage when it's stuck on like mentioned above. If you have full control voltage there, you need to trace it back to the culprit. If your equipment is 23 years old, it's probably operated by a rotary switch. I'm assuming changing the rotary switch position doesn't release the contactor when it's stuck...? Might be helpful to post equipment type and if you have credit cards or manual override controls. Still could be the contactor though. Another assumption - no other work has recently been done, right? If some work was recently done, that could help narrow down the cause as well.
No work has been done recently.
Will post equipment type...
Thanks
 
Etowah

Dan-Ark

Active member
Joined
Apr 22, 2018
Messages
261
Reaction score
45
Points
28
Location
Dover Arkansas
If turning off the breaker releases the contactor than I would bet on the coil staying energized (see above timers, switches, etc hints). If the contactor releases (you see the bar in the middle pop back out) then sadly, a new contactor may not fix it.
 