At one of my locations my Raypak Hot water boiler and holding tank are ready for the scrap yard. The wash has six bays and they’re set up at 4 gpm. Conceivably that is 24 gallons per minute of hot water needed and in Cleveland our incoming water can be as low as 40°. We typically set our hot water between 110 and 115° so that’s a rise of 70 to 75°. Is there a rule of thumb for figuring how many minutes out of an hour a pump may be on high pressure? This is by far our slowest wash so I’m thinking maybe 25%.
I’m thinking a smaller Phoenix HTP maybe the way to go. Just recently I had to replace a 120gal Storage tank at another wash and the tank alone was $1100 not including any fittings.