Taking this one step further...
My client noticed that every credit
transaction was billing even dollar amounts. This seemed odd because everybody doesn't stop their washing exactly at $5, $6, $7, etc.
Changing the
Nayax programming solved that issue. I changed the settings under Pulse/ccTalk from 100/60 to 25/15. Now the
transaction pricing on Count Up increments at 25c every 15 seconds instead of $1 every 60 seconds. (This client's car wash is priced at $3.00 to Start - $1.00 per Minute).
This location was also recently fitted with a Programmable Logic Relay to automate/mimic the touchscreen's STOP "button".
Big thanks to MEP001 for suggesting a simple wiring solution.
All unused contacts on the rotary switch's second stack are jumpered together to a single wire back to the equipment panel. The motor starter wires on the second stack are already in the equipment panel.
Those two 24vac hot wires connect to that bay's respective 2 inputs on the PLR.
When a customer selects OFF on the rotary switch, all 24v power to the 2 PLR inputs goes low (off).
This causes the PLR program to start it's 5 second countdown timer. The PLR's output then closes for 1 second, shorting the
Nayax Door Open wire to
Nayax Ground wire...Ending Charges.
Watch this clip for the "Auto Stop" solution. It's slicker than boiled okra!
View attachment IMG_1898(1).mp4