Tom,The single unloader is set at 1600psi. When the customer lets go of the trigger the VFD maintains either 1000 or 1400 depending on the pressure selected by the customer. The motor runs at about 15hz or so when the trigger is released since the flow is restricted. The transducer detects the pressure and it is wired to the VFD. The pressure doesn't hit the unloader pressure.
I can't believe you still think the dump gun is a good idea. Do you not realize that using a dump gun with a VFD pump system that if the customer is not pulling the trigger the tire cleaner will be dumping on the ground at around 4 gallons per minute?mjwalsh said:We like the type of gun (Cat has a version) that unloads around the outside of the nozzle when trigger is released. That way we have zero concern about heat building up in our unloader-regulator bypass hose. Do you think there is any chance the VFD would work with well with that type of gun.
Would you be able to provide the brand of transducer that you are using. I would like to build one of these systems.The single unloader is set at 1600psi. When the customer lets go of the trigger the VFD maintains either 1000 or 1400 depending on the pressure selected by the customer. The motor runs at about 15hz or so when the trigger is released since the flow is restricted. The transducer detects the pressure and it is wired to the VFD. The pressure doesn't hit the unloader pressure.
Thanks Tom for sharing your specific experience. There are a lot of vfds out there with different capabilities. I like to always have spare components on hand so I found this link potentially helpful:I've never had a capacitor fail and I'll bet it's because the vfds have a low duty cycle compared to the event you're talking about. VFD are popular in large buildings and run 24/7.
If you use a dump gun with a VFD and transducer the pressure drop would cause the motor and pump to run at full speed. I've never used a dump gun so I assuming that is the case.
The transducers we use are from www.transducersdirect.com and were a 0-2000psi 1/4" two wire 4-20 milli-amp.
That's exactly what it does. It's just like taking the tip out of the gun and pulling the trigger.thoffmanjr said:I'm assuming the dump gun opens up flow which would cause a huge pressure drop which would cause the speed to hit 60hz.
I think you're missing something too. It solves a problem of wanting lower pressure available to the customer by letting them vary it in a wasteful manner that can even be done with a standard trigger gun. The whole discussion started when someone wanted to REDUCE the use of their product and you suggested the dump gun which would only INCREASE the use. That complete lack of understanding of the particular issue shows a lack of logic in choosing to use dump guns in the bay at all.mjalsh said:I could be missing something ... but it seems like with programming the conditions of both the selection & the lessened pressure ma signal to the PLC could make it so a lower rpm could occur fast enough to avoid the unwanted 4 gpm that Mep referred to.
Only a small percentage of the time do the customers let up on the trigger during the high pressure. When they do it is less pressure but not the "all or nothing" like you describe. The increased volume during those times it is not that drastic. The Flojets for the tire motor & presoak with air actually makes for more of a foaming experience which helps the customer with the "dwell factor". As far as more waste ... it is not even close to how you describe with our specific Flojet low pressure-air combination from our two 6 solenoid manifolds. Softsuds as shown below was was seeking to understand similar to myself ... how the VFD driven pump can function with the proper controls ... specifically with the low pressure chemical... being drawn in the pump or premixed. If the VFD-controls makes the motor-pump go to an almost idle state when that type of low pressure selection is made ... then it seems like it could perform similar to the way our Flojets do. At no time did I state that I knew the VFD has that capability like the Flojet. Like Softsuds ... that is why I was asking hoping that someone had tinkered a bit VFD wise & saw first hand & documented exactly how the volume varies with the pressure & the slightly increased nozzle area opening ... based on the Flojet less than 100 psi similar level.That complete lack of understanding of the particular issue shows a lack of logic in choosing to use dump guns in the bay at all.
Softsuds,When using a Single Hose or Single Hose VFD system, do the low pressure chemicals go into the pump at application strength or are they mixed at the pump head with fresh water and diluted there ?
Thanks
The pressure is controlled by the VFD based on FLOW. It ramps the pump speed up (increasing flow) until the desired pressure is met. Your dump gun doesn't allow "a bit more flow," it allows the full capacity of the pump to be dumped around the tip. That means the flow to achieve 50 PSI can never be met even with the pump running at full RPM. It's not an issue with your FloJet system because there's presumably a needle-valve adjustment in the room preventing more flow when the dump gun is opened. It is once again not relevant to this situation.mjwalsh said:it does appear that Tom gets the VFD-motor driven pump down to 50 psi for his unique flush approach.
Mep & other VFD-Pump experts,The pressure is controlled by the VFD based on FLOW. It ramps the pump speed up (increasing flow) until the desired pressure is met. Your dump gun doesn't allow "a bit more flow," it allows the full capacity of the pump to be dumped around the tip. That means the flow to achieve 50 PSI can never be met even with the pump running at full RPM. It's not an issue with your FloJet system because there's presumably a needle-valve adjustment in the room preventing more flow when the dump gun is opened. It is once again not relevant to this situation.
You're mistaken. The transducer, along with the VFD, is also the pressure regulator. In order to make pressure, you need flow and a restriction. With a dump gun, rather than increasing the restriction when the trigger is released the restriction is reduced. The pump will speed up to try and achieve the pressure programmed into the controls.mjwalsh said:I believe Tom's approach is using a transducer for pressure monitoring mainly to allow for a slightly lower pressure as a choice.