My dated hot water production boiler cannot keep up with my demand on busy days in the automatic. I have talked with Washworld and they recommend a 6 GPM unit for the pre soak passes at about 120 degrees. I would be uaing natural gas and would like to hear some recommendations for a high efficiency unit.

Thanks!

John
 

Kirb

Member
Joined
Nov 1, 2007
Messages
203
Reaction score
5
Points
18
Location
_
John,
Turn your boiler up and put in a mixing valve.
 

Sudzie

New member
Joined
Sep 18, 2011
Messages
28
Reaction score
0
Points
1
Location
York Maine
We run both of our washes with only Rinnai heaters. 3 at one (softtouch cloth tunnel) and 2 at the other (touchless tunnel) Work Great at both washes. If you have a on board unit I would pre feed with the Rinnai. The LS 94i has a flow rate of up to 7 gpm and 140 high temp. Full disclosure we also opperate a oil & propane co.
 
Etowah

pitzerwm

Active member
Joined
Aug 28, 2007
Messages
3,693
Reaction score
10
Points
36
Location
Tri-Cities, WA
Have you thought about the PreSoak eating up the heater. On my unit it used a tank with a hot water type heater, then pumped it out. Worked fine.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Have you thought about the PreSoak eating up the heater. On my unit it used a tank with a hot water type heater, then pumped it out. Worked fine.
I was only intending to feed the sta-rite pump, not run the actual solution through it. Am I missing a fundamental characteristic of these systems?
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
Bubbles,
My M5 has an electric one that keeps up...but electric not good.

A tankless might be good if you can feed the hot water from it into the existing one so that the delivery is as instant as possible.

Rinnai's...I have 8. They work well but I feel have a design flaw IMHO. The electronics were mounted at the bottom and the heat exchange above. I had an exchanger leak and ruined the electronics :( The Takagi's electronics are on top. The Rinnai's are also more expensive.

I really like my new NTI boiler (available thru Kleenrite). Glow plug fired, great modulation and can pump way more heat per BTU rating than the Rinnais.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Bubbles,
My M5 has an electric one that keeps up...but electric not good.

A tankless might be good if you can feed the hot water from it into the existing one so that the delivery is as instant as possible.

Rinnai's...I have 8. They work well but I feel have a design flaw IMHO. The electronics were mounted at the bottom and the heat exchange above. I had an exchanger leak and ruined the electronics :( The Takagi's electronics are on top. The Rinnai's are also more expensive.

I really like my new NTI boiler (available thru Kleenrite). Glow plug fired, great modulation and can pump way more heat per BTU rating than the Rinnais.
Thanks for the feedback Big. I have a cold water feed for my auto and I was going to use that to feed the on demand heater that would feed directly into the sta-rite pump. Does that make sense?
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
Thanks for the feedback Big. I have a cold water feed for my auto and I was going to use that to feed the on demand heater that would feed directly into the sta-rite pump. Does that make sense?
Well...its just delivery time. So the tankless has to fire and generate hot water, then its gotta bleed to the tip of the arch. That might take too long... You might need to put a small electric heater ahead of it to get quick hot water while the tankless gets going.
 
Etowah

Sudzie

New member
Joined
Sep 18, 2011
Messages
28
Reaction score
0
Points
1
Location
York Maine
You just need to put in a circ. pump and have it come on for a bit prior to use. Pm me and I can send pictures of our touchless tunel presoak arches. Chem is not a problem along with air injection. We have our circ. come on when the conveyor starts up. We have a 25 ft run to the arch and it takes 12 seconds for 135*f water to be at the head of the arch. 3628 cars washed in February this year on 387 gals of LPG. Came out to about .30 cents per car for the whole wash.
 

bigleo48

Active member
Joined
Sep 6, 2007
Messages
1,887
Reaction score
0
Points
36
You would need to do some configuring for this to work as most Tankless units require .5 gallon draw before they fire. So you would need a bigger circ pump that fires when wash is activated by the entry system.

My tankless on my IBA side actually have a small tank, so my circ pump works for my pet washes.
 

Sudzie

New member
Joined
Sep 18, 2011
Messages
28
Reaction score
0
Points
1
Location
York Maine
You would need to do some configuring for this to work as most Tankless units require .5 gallon draw before they fire. So you would need a bigger circ pump that fires when wash is activated by the entry system.

My tankless on my IBA side actually have a small tank, so my circ pump works for my pet washes.
You are correct on the .5gpm flow for it to turn on. But with that said most taco models are close to the same price .25 to 3.0 gpm. We found that a 1.0 works fine and use the one that is stainless wet end. Make sure you have a feed check valve and a return flow check installed.
 

tobaccofarmer

Member
Joined
Sep 7, 2007
Messages
154
Reaction score
0
Points
16
You could plumb 2 together to achieve greater flow, All I did was plumb 1 and have it feed a 60 gallon electric water heater, that way I have a greater amount of hot water ready and available. The instant feeds the electric which just keeps it hot 120ish and I always have plenty of hot water. Never had an issue with not having enough!
 

JIMT

Member
Joined
Sep 4, 2007
Messages
143
Reaction score
0
Points
16
Location
Toledo, Oh.
But with that said most taco models are close to the same price .25 to 3.0 gpm. We found that a 1.0 works fine and use the one that is stainless wet end. Make sure you have a feed check valve and a return flow check installed.
__________________
The Auto Spa Car Wash
York & Kittery, Maine

What are taco models with the stainless wet end? Your other post said that you use Rinnia and it costs 30 cents per car. Is that to just heat the presoak?

Thanks
JIMT
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
So I think I have found the heater I am going to use. Since I am still going to feed this tankless unit with the water from my boiler storage tank, the temperature rise needed at most will be roughly 60 degrees. This should allow me to maintain my flow rate while still getting optimal temperature right at the feed out to the wash arch. It's a Takagi high efficiency unit that I can get from Dultmeier for about $1,200. Anyone see any issues why this wouldn't work?

Thanks!

John
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
It may have a flow restriction device that reduces the flow through the unit until it builds to the temp you have it set for. That could be a problem since your boiler is already having issues keeping up with demand. If it falls behind, you won't have the flow you need for your presoak.

I'd try and find a solution that takes the load off the existing boiler entirely.
 

Sudzie

New member
Joined
Sep 18, 2011
Messages
28
Reaction score
0
Points
1
Location
York Maine
But with that said most taco models are close to the same price .25 to 3.0 gpm. We found that a 1.0 works fine and use the one that is stainless wet end. Make sure you have a feed check valve and a return flow check installed.
__________________
The Auto Spa Car Wash
York & Kittery, Maine

What are taco models with the stainless wet end? Your other post said that you use Rinnia and it costs 30 cents per car. Is that to just heat the presoak?

Thanks
JIMT
Taco 008 stainless for each pre soak arch (we have two of them) and the .30 CPC includes tunel heat. 2/ 60 ft verberay (sp) tube heaters from airlift. We did have a warm February.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
It may have a flow restriction device that reduces the flow through the unit until it builds to the temp you have it set for. That could be a problem since your boiler is already having issues keeping up with demand. If it falls behind, you won't have the flow you need for your presoak.

I'd try and find a solution that takes the load off the existing boiler entirely.
I'm trying to stay under 200k btu's to keep from having to have another boiler inspection. I may be able to call Takagi and see if they have a flow restrictor on there. Good advice, thanks!
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Okay, I have my Takagi TH-2 plumbed with the water feed lines and gas lines. I'm trying to understand if regular schedule 40 pvc is sufficient for the exhaust piping for this unit? I thought I could use regular pvc, but want to check here before I go and spend the time and effort. FYI, I did call a local company and they wanted to charge me a service call fee...
 