simulated pulse issue

goldberg

New member
Joined
Jun 26, 2013
Messages
2
Reaction score
0
Points
1
Location
mahopac ny
hello everyone. im a newbie here! Im having an issue with my simulated pulse staying on. its a drb system. ive gone to O and press acknowledge button and shut it off yet it continues to flash simulated on. drb says it might be a bad censor. anyone experience this problem and what the solution might be?
 

Washmee

Fullservice Tunnel
Joined
Sep 3, 2007
Messages
973
Reaction score
2
Points
18
Location
Canton, Ohio
Have you repaired the issue that caused you to turn on the simulated pulse? Are you sure you are actually turning it off. Use the enter button to highlight the option in other operations page that says enable/disable simulated pulse. Use the =/- key to toggle between on and off. If you are toggling the simulated switch to off, you would be seeing pulses from the actual pulse switch at that point. If you turn it off and don't see any pulses on the tunnel status screen when the conveyor is running then the actual pulse switch is not working. What type of pulse switch do you have?
 

Earl Weiss

Well-known member
Joined
Aug 31, 2007
Messages
6,337
Reaction score
917
Points
113
hello everyone. im a newbie here! Im having an issue with my simulated pulse staying on. its a drb system. ive gone to O and press acknowledge button and shut it off yet it continues to flash simulated on. drb says it might be a bad censor. anyone experience this problem and what the solution might be?
Use the enter button to highlight the option in other operations page that says enable/disable simulated =/- key to toggle between on and off<<<

As he said Acknowledging errors will not turn sim pulse on or off. You were on sim pulse because?
 

goldberg

New member
Joined
Jun 26, 2013
Messages
2
Reaction score
0
Points
1
Location
mahopac ny
I don't know what initially turned on the sim pulse. all I know is that I now cant shut it off. btw, everythinbg in my system is working fine. my hydro blasters are working fine measuring the cars. the system is seems to be measuring the cars fine.
 

Earl Weiss

Well-known member
Joined
Aug 31, 2007
Messages
6,337
Reaction score
917
Points
113
I don't know what initially turned on the sim pulse. all I know is that I now cant shut it off. btw, everythinbg in my system is working fine. my hydro blasters are working fine measuring the cars. the system is seems to be measuring the cars fine.
That is probably because it is your enter switch that measures the car. As long as the conveyor is set to the correct speed, it will start and stop functions at the correct time. Just don't adjust the conveyopr speed.
 

Washmee

Fullservice Tunnel
Joined
Sep 3, 2007
Messages
973
Reaction score
2
Points
18
Location
Canton, Ohio
On the main tunnel status screen are you getting a scrolling message that says "Simulated Pulse Enabled" ? Also on that screen there is an indicator light for the pulse switch. When the conveyor is running does that light blink?
 