Anti Siphon Valve

CarWashBoy

Active member
Hi.. I'm planning on moving my chemicals upstairs.. so pumping station down stairs and chemical upstairs .. I'm concerned about siphoning.. does anyone have info on a anti siphoning in line valve? or another solution or idea?
Thanks in advance..
Doug
 
If you're planning to feed Hydrominders from chemical containers upstairs, I don't think you'll have much luck. You could add a siphon breaker at the highest point, but the line going down will still drain out every time the tank fill stops.
 
As long as you are moving the soap upstairs, which means you have easy access, why not take the mixing tank up there also? Then your lines will run to solenoids and no more siphon.
 