I have 60 psi coming into my car wash via a 2" supply line. There is a 15 psi pressure drop across my Watts RPZ 909 backflow preventer.
I am now getting a low pressure trip on my RO machine when all of my pumps kick on during busy days.
Isn't this amount of pressure drop excessive? Would a rebuild (seals only or what?) help?
Has anyone rebuilt a RPZ unit? It doesn't look to tough after looking at the diagrams.
I am now getting a low pressure trip on my RO machine when all of my pumps kick on during busy days.
Isn't this amount of pressure drop excessive? Would a rebuild (seals only or what?) help?
Has anyone rebuilt a RPZ unit? It doesn't look to tough after looking at the diagrams.