So I changed the contractor on self serve bay, all the low pressure would come on but high pressure pump would not engage on if we put the quarters from the bay but it’s comes on when we push the button in contacter.
any suggestions?
So I changed the contractor on self serve bay, all the low pressure would come on but high pressure pump would not engage on if we put the quarters from the bay but it’s comes on when we push the button in contacter.
any suggestions?
Assuming you wired the "contactor" correctly, check that your 24 VAC transformer is functional for that bay.
Then check the wiring all the way to the rotary switch in that bay, and back to the contactor.
So I changed the contractor on self serve bay, all the low pressure would come on but high pressure pump would not engage on if we put the quarters from the bay but it’s comes on when we push the button in contacter.
any suggestions?
Assuming you wired the "contactor" correctly, check that your 24 VAC transformer is functional for that bay.
Then check the wiring all the way to the rotary switch in that bay, and back to the contactor.
I'm still a little unclear about the real problem and what you have tried. Pictures would be enormously helpful.
On three phase pumps there is typically a contactor and overload that are separate components but attached together into one solid unit. The overload is what would "trip" and kill voltage the contactor coil. it has to be reset and wired properly to allow voltage to travel to the contactor
Is the new contactor the right coil voltage? You likely need 24 Volt AC coil on the contactor. If you have a multimeter you should be able to detect 24 volts on the small wires going into the contactor
On the rotary switch in the bay is two "stacks" or levels of terminals. One stack with all the wires connected is usually low pressure things and the second stack that only has a few connections on it is reserved for the high pressure pump. Make sure one of those wires hasn't come loose.