I have a older dilling harris self-serve system from like 89'. My circuit breaker for one bay continued to to trip almost daily. So after some problem solving I determined it was my motor starter. I went to Grainger and bought a replacement and now every time I go to a high pressure function at my bay my timer resets continually (breaker stay's on fine). I am at a loss as to what is causing this after 3 hours of trouble shooting. So I figure I would post it on here. I am thinking it has something to do with the 24 volts on the motor starter that I hooked up wrong because when I press the motor starter manually it runs fine. Thanks in advance for the help.
 

sparkey

Active member
Joined
May 22, 2010
Messages
905
Reaction score
187
Points
43
Location
Ohio
Its not a case of your meter box is 24 volts AC and the contactor is 24 volts DC is it?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
You've got something hooked up wrong with the control voltage, or the coil of the new contactor is the wrong voltage as sparkey said.

Just out of curiosity, how did you determine the motor starter was the cause of your breaker tripping?
 

waterway

Member
Joined
Feb 18, 2010
Messages
97
Reaction score
0
Points
6
Location
Jupiter, FL
I figured it was the motor starter because in my past with these systems whenever the breaker keeps tripping its always been either the breaker or the motor starter. I'm thinking you might be right about the ampridge. I'm going to check it now.
 
Joined
Nov 9, 2007
Messages
330
Reaction score
1
Points
16
Location
CT.
I figured it was the motor starter because in my past with these systems whenever the breaker keeps tripping its always been either the breaker or the motor starter. I'm thinking you might be right about the ampridge. I'm going to check it now.
Did it only trip when you used a hp function and if so what function, the starter may be fine but a sol may be the problem
 

Kevin James

Active member
Joined
Nov 15, 2007
Messages
562
Reaction score
32
Points
28
Did you replace the motor starter with the same motor starter, part number etc.? Or did you buy another brand, model?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
waterway said:
I'm thinking you might be right about the ampridge.
We're referring to the coil VOLTAGE. It will be marked on the top of the contactor and should read "24V 60Hz".
 

ken-pro

Equipment Distributor
Joined
Aug 31, 2007
Messages
140
Reaction score
2
Points
16
Location
Kitchener, Ontario
My guess is that the coil voltage of the new contactor does not match the voltage of the old one - Like MEP suggested
 