What's new

Feed Water Pressure and Watts Regulator

Joined
Nov 13, 2017
Messages
315
Reaction score
15
Points
18
Location
Calgary
Hello, I noticed pressure on the gauge where city water comes to the SS solenoid before they go to the hot water tank is about 80 psi, while usually not that high. (see pics) Would this create problems? When I played with the regulator (after 4 years), it seems to be nicely staying at about 20-30 psi depending on how many pumps are running. If I need to change the Regulator, where do you buy it from? Coleman Hanna price is crazy high.

Also how often do you change these? every 20 years? It seems to be very painful to change it. The whole mechanism need to be removed. and dismantled since they are all so close to each other. which tells me I probably end up breaking more stuff than fixing this. So I might just leave it alone until I see serious issue.

I also see increase in pressure in my spot free gauges. Perhaps the whole city pressure increases sometimes? and the problem is somewhere else? I'm not even sure if there is a problem lol. Can it be the big back pressure valve ? but that valve is 100% open all the time.
 

Attachments

Last edited:

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,131
Reaction score
585
Points
113
Location
CO
PRVs aren't cheap
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
I'm not sure why there's a regulator on that line unless it's for the weep. IIRC the solenoids are rated for 150 PSI MOPD, so 80 won't bother them. I've taken the regulator out on that system when it has failed. The pressure to the spot free from the city doesn't affect anything since it uses a Procon pump. Inlet pressure doesn't change the output pressure.

Edit: The max inlet pressure rating for Cat 5CP2120W pumps is 60 PSI, so the regulator does serve a purpose. You certainly don't have to get it from Coleman or even stick to one with that range, as long as you can set it below 60 PSI.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
That is a backflow preventer, not a regulator. It's pretty easy to rebuild, but if you expect to replace all the internal parts you're almost better off replacing the whole valve IMO. Mine is leaking badly, and a total rebuild is only $50 less than a new unit.
 
Joined
Nov 13, 2017
Messages
315
Reaction score
15
Points
18
Location
Calgary
That is a backflow preventer, not a regulator. It's pretty easy to rebuild, but if you expect to replace all the internal parts you're almost better off replacing the whole valve IMO. Mine is leaking badly, and a total rebuild is only $50 less than a new unit.
Mr. MEP001 I just love your responses here. Sometimes I tend to try to make my carwash a perfect one, and I know I will end up making it worse. I just need to close my eyes and pass.
 

PaulLovesJamie

rural 5 bay SS
Joined
Aug 30, 2007
Messages
1,321
Reaction score
229
Points
63
Location
Kutztown PA
If I need to change the Regulator, where do you buy it from? Coleman Hanna price is crazy high.
I'm not familiar with your setup so perhaps someone else can chime in, but I dont see a bypass hose coming off that watts, so I think you could replace it with a simpler - and therefore much less expensive - model?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
I'm not familiar with your setup so perhaps someone else can chime in, but I dont see a bypass hose coming off that watts, so I think you could replace it with a simpler - and therefore much less expensive - model?
It's a Coleman Super Saver, that manifold has the rinse solenoids and weep on it. It's just a simple inline regulator like this one:


 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
It definitely doesn't need to be a $535 regulator. See what the MOPD rating of the solenoids are, and whatever you replace it with just needs to adjust below that pressure.
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,883
Reaction score
2,260
Points
113
When I was a young man I was a state certified backflow tester/instructor. I repaired a lot these backflow unit so they would pass the yearly inspect/test. When was the last time this unit was tested? Open it up and look for any debris inside primarily under the rubber check valves. You can flip over the rubber on check valve to get more life out of them. If you have to replace it replace it with a Zurn Wilkins 975XL, the parts are less expensive and they are easier to work on. I'd replace the regulator with a Wilkins, they are less expensive. I've never been a big fan of Watts products.
 

Keith Baker

Keith Baker
Joined
Sep 19, 2007
Messages
202
Reaction score
95
Points
28
Location
Omaha, NE.
I didn't see anyone mention an expansion tank. At my place an expansion tank is required because I have a stored hot water system with backflow valves. When the water heats it builds up pressure because the backflow won't let it release to the city system. If the tank has failed then the water pressure could do what your describing. Do you have a tank like this in the area of the hot water tank? https://www.supplyhouse.com/Amtrol-...MIhdv5nOqB8AIVDfDACh23WgAwEAYYASABEgLW3_D_BwE
 

srr5008

Member
Joined
Mar 2, 2015
Messages
96
Reaction score
36
Points
18
Location
Northeast PA
We just replaced our Watts regulator $450 for a 1.5" unit.

Unfortunately we've had to replace it several times in the last 10 years - we will be looking at a different brand (possibly Zurn, as suggested above by Randy). We seem to have problems with the pressure creeping (doubling) with ours after a few years of use.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,691
Reaction score
1,437
Points
113
Location
Ohio
I'm just speculating here but could it be that you have a more than normal amount of abrasive sediment coming in that is wearing the seals quick?
 

Greg Pack

Wash Weenie
Joined
Sep 3, 2007
Messages
4,412
Reaction score
2,219
Points
113
Location
Hoover, Alabama
We just replaced our Watts regulator $450 for a 1.5" unit.

Unfortunately we've had to replace it several times in the last 10 years - we will be looking at a different brand (possibly Zurn, as suggested above by Randy). We seem to have problems with the pressure creeping (doubling) with ours after a few years of use.

Yeah.my watts 2" is not lasting long at all-maybe a year. City Pressure is close to 150 psi.Will regulate but pressure creeps back up when the flow stops. I understand for longevity I need two in series to stage the pressure down.
 
Joined
Dec 4, 2007
Messages
651
Reaction score
4
Points
18
Location
Central Texas
Hello, I noticed pressure on the gauge where city water comes to the SS solenoid before they go to the hot water tank is about 80 psi, while usually not that high. (see pics) Would this create problems? When I played with the regulator (after 4 years), it seems to be nicely staying at about 20-30 psi depending on how many pumps are running. If I need to change the Regulator, where do you buy it from? Coleman Hanna price is crazy high.

Also how often do you change these? every 20 years? It seems to be very painful to change it. The whole mechanism need to be removed. and dismantled since they are all so close to each other. which tells me I probably end up breaking more stuff than fixing this. So I might just leave it alone until I see serious issue.

I also see increase in pressure in my spot free gauges. Perhaps the whole city pressure increases sometimes? and the problem is somewhere else? I'm not even sure if there is a problem lol. Can it be the big back pressure valve ? but that valve is 100% open all the time.
just changed ours due to it busted in the freeze, $125.00 dollars
 
Joined
Dec 4, 2007
Messages
651
Reaction score
4
Points
18
Location
Central Texas
Hello, I noticed pressure on the gauge where city water comes to the SS solenoid before they go to the hot water tank is about 80 psi, while usually not that high. (see pics) Would this create problems? When I played with the regulator (after 4 years), it seems to be nicely staying at about 20-30 psi depending on how many pumps are running. If I need to change the Regulator, where do you buy it from? Coleman Hanna price is crazy high.

Also how often do you change these? every 20 years? It seems to be very painful to change it. The whole mechanism need to be removed. and dismantled since they are all so close to each other. which tells me I probably end up breaking more stuff than fixing this. So I might just leave it alone until I see serious issue.

I also see increase in pressure in my spot free gauges. Perhaps the whole city pressure increases sometimes? and the problem is somewhere else? I'm not even sure if there is a problem lol. Can it be the big back pressure valve ? but that valve is 100% open all the time.
Isnt that for the weep system?
 
Top