Heater is running too much...

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
Here is a picture of the heater I am using for both the equipment room and the dog wash...

Hanging Heater

I have the stat set at 62 degrees, but the heater is still running far too much and I'm concerned that my gas bill is going to go through the roof if I'm not careful. Does anyone have any suggestions as to how I could help retain some of the heat that I am losing in my equipment room and the dog wash?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
You should have a return vent from the dog wash to the equipment room. If you don't, all the heated air pumped into the dog wash has to get forced out through gaps and is replaced by cold air sucked into the equipment room, then instead of reheating warm air you're heating fresh cold air.
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
I do have a cold air return...that has helped, but that heater is running about 10 times an hour and just isn't performing very efficient due to the heat loss...
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
You might have to make the equipment and pet wash rooms as air-tight as possible so the air circulates between them and doesn't get lost.
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
6,046
Reaction score
1,685
Points
113
Location
Orange, MA
My equipment room is not well insulated at att.

But with my 2 Raypaks running in there and floor heat set at 46F and slab temp at 41F it stays 50F in there even when it's 12F out like last night.

How hot do you need your e.r.? You do have floor heat, right?
 
Etowah

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,297
Reaction score
753
Points
113
Location
Leominster, MA
10 times an hour?
Sounds like it may be short cycling. Is the room coming up to temp before it shuts off? Where is the t-stat in relation to the air coming out of the vent?
I've never seen a modine heater with ductwork attached. Is there a high limit between the coils and the duct? Is it overheating and tripping out then cooling down allowing the heater to cycle on/off?
 

Bubbles Galore

Active member
Joined
Apr 11, 2008
Messages
2,115
Reaction score
0
Points
36
Location
Michigan
I am not too concerned about the equipment room as much as I am about the comfort of my customers in the dog wash. In one of my "dimmer" moments, I mounted the thermostat about 5-6' away from the incoming duct. It is set at 62 and has a +/- 1 differential. I wonder if I could set a range from say 63-58 that it would fire until it reached 63 and then wouldn't cycle until it hit 58...thoughts? Is something like that even feasible?
 

pitzerwm

Active member
Joined
Aug 28, 2007
Messages
3,693
Reaction score
10
Points
36
Location
Tri-Cities, WA
IMO open up the differential in the stat and move the stat so the air flow doesn't affect it.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
You won't use less gas if it runs twice an hour for five minutes each time instead of ten times an hour for a minute each time.

If you don't need the heat in the equipment room, you could build a box around the heater so the air only circulates to heat the pet wash room.
 