What's new

Hoping for help troubleshooting a Jim Coleman self serve tri foam conditioner unit.

doublj70

Member
Joined
Apr 16, 2008
Messages
53
Reaction score
1
Points
8
Location
California
Hello,
I have a Jim Coleman self serve tri foam conditioner system that I have had in use for like 15 years, with very few problems. Yesterday I found it not working. the controller has power and when you select it in the bay, that bay lights up on the controller, but the procon pump motor doesn't come on. The procon pump motor does come on and sounds fine if I manually push down the contactor. So it seems like the coil that turns on the contactor isn't working or not getting power. I don't have the wiring diagram, so I'm not sure it the controller powers the contactor coil or if there is a relay or something in between. Has anyone had this problem? Any advise would be greatly appreciated!

Thanks!
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
I'm running a wash where the controller has failed and been bypassed. Just order an IDX MX-8 or something equivalent, run the trifoam wires to its inputs along with a common, supply it with 120V AC and run that to the contactor.
 

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,131
Reaction score
582
Points
113
Location
CO
If memory serves, JCC used Omron Programmable Logic Relays with the outputs powering ice cube relays for the motor contactor.
The PLR might be "mentally" locked up. Try cycling power to the PLR.
 
Top