What's new

Hot water temp? Input tankless vs tank water heating system

cap732000

Member
Joined
Apr 7, 2014
Messages
172
Reaction score
4
Points
18
Location
oklahoma
Looking at changing my boiler to a on demand system. Any body have any input on these and what temp typically do you washers out there keep yours at. Tankless vs tank???? Any input be great!
 

rph9168

Carwashguy
Joined
Aug 31, 2007
Messages
2,663
Reaction score
11
Points
38
Location
Atlanta
As far as water used when mixing the chemicals do not go over 120.
 

soapy

Senior Member
Joined
Sep 1, 2007
Messages
2,896
Reaction score
855
Points
113
Location
Rocky Mountains
Be sure to check the flow rate. If you have 4 ss bays that can use 3.5 gpm you will need a boiler to flow 14 gpm if you are only using one boiler.
 

cap732000

Member
Joined
Apr 7, 2014
Messages
172
Reaction score
4
Points
18
Location
oklahoma
Ok help me out I'm running #5 tip at 1500psi I think that puts me at about 3.1 gpm I'm thinking without checking chart I was thinking of putting 1 instant for two bays at 7 gpm.
 
Top