I usually try not to ask the obvious questions, but you did restrict the DEMA to make it draw? I don't know what model you used, but the ones with a variable flow have to be trimmed to your flow or you'll never create a suction.
 

traveler17

Well-known member
Joined
Nov 5, 2019
Messages
861
Reaction score
693
Points
93
Location
SE NC
I usually try not to ask the obvious questions, but you did restrict the DEMA to make it draw? I don't know what model you used, but the ones with a variable flow have to be trimmed to your flow or you'll never create a suction.
yeah these do not need a trimmin’
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,860
Reaction score
2,211
Points
113
That's really odd. I've been using DEMA 203C injectors on my self serve equipment for well over 30 years, they still work fine. I should probably change out the internal nozzle.
 

traveler17

Well-known member
Joined
Nov 5, 2019
Messages
861
Reaction score
693
Points
93
Location
SE NC
That's really odd. I've been using DEMA 203C injectors on my self serve equipment for well over 30 years, they still work fine. I should probably change out the internal nozzle.
I do have another on the way along w the hydra flex, which I use for the pre soaks but yeah I’ve never had an issue. Only thing I can guess is they are faulty. Gotta be it, I mean I hope that’s it :)
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
I doubt they are faulty... It's about the flow rate. The dema has a wide flow rate range and the nozzle bushings are what narrow it down so that it can create a venturi (unless you are using a b model which has a bypass screw to adjust as mep said). Since you were able to get suction from a 5.5 injector, chances are you didn't have enough flow for the dema. A smaller dema should have worked, or more flow should have worked. As Hoskins mentioned, usually that's caused by a faulty open solenoid on another product plumbed in parallel to the one giving you problems. On a Belanger, the flow is pump speed adjustable. But on other equipment, usually the air pressure setting causes too much backpressure to maintain accurate injector flow rates.
 
Last edited:

Greg Pack

Wash Weenie
Joined
Sep 3, 2007
Messages
4,391
Reaction score
2,169
Points
113
Location
Hoover, Alabama
Yeah, I'm old school and kinda still like hydrominders. Any change in product flow rates (clogged nozzles, too much air, etc)can throw the injectors off.
 

traveler17

Well-known member
Joined
Nov 5, 2019
Messages
861
Reaction score
693
Points
93
Location
SE NC
I doubt they are faulty... It's about the flow rate. The dema has a wide flow rate range and the nozzle bushings are what narrow it down so that it can create a venturi (unless you are using a b model which has a bypass screw to adjust as mep said). Since you were able to get suction from a 5.5 injector, chances are you didn't have enough flow for the dema. A smaller dema should have worked, or more flow should have worked. As Hoskins mentioned, usually that's caused by a faulty open solenoid on another product plumbed in parallel to the one giving you problems. On a Belanger, the flow is pump speed adjustable. But on other equipment, usually the air pressure setting causes too much backpressure to maintain accurate injector flow rates.
Agree w everything you said which is why I’m stumped. Put the exact 204 C on and the same bushing. Replaced 1 valve parallel to it that was leaking. I agree I’m losing the flow to create the draw but I’m just not sure where.
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
Belanger units usually have ball valves under the solenoids. Have you tried turning off every one except the one with the injector? Does it appear to be putting out a full spray of water in the bay?
 

traveler17

Well-known member
Joined
Nov 5, 2019
Messages
861
Reaction score
693
Points
93
Location
SE NC
Belanger units usually have ball valves under the solenoids. Have you tried turning off every one except the one with the injector? Does it appear to be putting out a full spray of water in the bay?
Actually I didn’t and I don’t know why. I’ll do that today and yeah the arms are putting out the normal psi I had prior to the problem. Thank you for the advice!
 

traveler17

Well-known member
Joined
Nov 5, 2019
Messages
861
Reaction score
693
Points
93
Location
SE NC
Belanger units usually have ball valves under the solenoids. Have you tried turning off every one except the one with the injector? Does it appear to be putting out a full spray of water in the bay?
Hey J , just an update I closed the 3 ball valves and left the wax option open and still have no draw and same pressure I’ve always had in the arm manifolds. Very odd. Appreciate the try
 

JGinther

Zip-tie engineer
Joined
May 31, 2008
Messages
743
Reaction score
170
Points
43
Location
Loveland, CO
At a high enough flow, the injector has to work (if its plumbed in right). By work, I mean create vacuum - it just a matter of the fluid dynamics and the shape of the part. So, either there isn't suction because there isn't enough flow (a myriad of possibilities), or the injector ball/spring is stuck.
 

traveler17

Well-known member
Joined
Nov 5, 2019
Messages
861
Reaction score
693
Points
93
Location
SE NC
At a high enough flow, the injector has to work (if its plumbed in right). By work, I mean create vacuum - it just a matter of the fluid dynamics and the shape of the part. So, either there isn't suction because there isn't enough flow (a myriad of possibilities), or the injector ball/spring is stuck.
Gotcha. I appreciate the input!!
 