During busy times I'm experiencing hot water shortages in my dog wash. I was wondering what you guys thought could be a remedy?

Some kind of pressurized heated holding tank? Something else?

Thanks.
 

PrecisionPyro

Member
Joined
Dec 3, 2020
Messages
42
Reaction score
39
Points
18
Location
West Michigan
Point of use tankless might be a buffer for you. It would not kick in until water temp drops below set point, then will kick back off as temps come up or customer ends wash. They offer smaller 110v ones for a couple hundred bucks.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,653
Reaction score
1,413
Points
113
Location
Ohio
During busy times I'm experiencing hot water shortages in my dog wash. I was wondering what you guys thought could be a remedy?

Some kind of pressurized heated holding tank? Something else?

Thanks.

What do you have now and is it dedicated to the dog wash or integrated into the car wash?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
I'd add another unit for just the dog wash. That's where you really don't want to run out of hot water. The car wash customers most likely will never notice. This is assuming you're not running low on flow. If that's the case, you might want to add a couple units or a storage tank and a recirculation pump to the heater.
 

soapy

Senior Member
Joined
Sep 1, 2007
Messages
2,896
Reaction score
855
Points
113
Location
Rocky Mountains
You might also check to see if you could eliminate some functions that are taking hot water that may not really need it. Hot water RInse?
 

Car_Wash_Guy

Well-known member
Joined
Apr 6, 2015
Messages
1,175
Reaction score
349
Points
83
Location
out west
I'd add another unit for just the dog wash. That's where you really don't want to run out of hot water. The car wash customers most likely will never notice. This is assuming you're not running low on flow. If that's the case, you might want to add a couple units or a storage tank and a recirculation pump to the heater.
The thing that is puzzling to me is that I have ~600g of HW storage. During busy times I lose not only HW but also pressure in the dog wash.

The only other things that are using HW is : HW holding tank and the HW tank for chemicals for my touchless
 

Earl Weiss

Well-known member
Joined
Aug 31, 2007
Messages
6,372
Reaction score
943
Points
113
If I send straight hot water only to areas I will mot have enough - however water does not to be that hot. Just warm to the touch is enough, so I "T" in cold water that I can adjust thru a gate valve blending im less cold in colder weather and more in warmer weather. This reduces the Hot water volume being used.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
The thing that is puzzling to me is that I have ~600g of HW storage. During busy times I lose not only HW but also pressure in the dog wash.
You'll need to find the point of loss in pressure. It could be from the city, after a failing RPZ valve, your softener, or even a bad gate valve. I always start with gauges on the RPZ valve which will immediately confirm or eliminate city supply and the valve.
 

Starrwash

Member
Joined
Nov 24, 2018
Messages
83
Reaction score
27
Points
18
Location
Zumbrota Minnesota
I purchased the small 110v electric tankless hot water heater at Home Depot and installed close to the dog wash. So I take hot water from primary heater pipi to small electric and to dog wash. No delay in water temperature at wash.
 