What's new

lag time when switching options in SS

audiosnow46

Member
Joined
Feb 13, 2011
Messages
63
Reaction score
0
Points
6
Location
Rapid City, SD
Good morning all,

Let's say I put my $2.50 to start my wash, turn the knob to pre-soak. It takes about 30-45 seconds just to get to the hose. Both bays are next to control room. Then i switch to rinse it takes about that 30-45 sec to clear the lines... I went to a competitior in town to see how fast theres switched over and it was within 5 seconds... makes me sick thinking i am 9 times longer of a wait. Is there a special pump of something you use or i guess im unsure how it even really works. any input would be appreciated. Thanks!
 

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,840
Reaction score
444
Points
83
Location
Ohio
My Low Pressure Functions are "T"d into the High Pressure line right above each bay using a manifold. Sounds like your's is "T"d at the pump? Having them above the bay shortens the amount of time it takes to get to the gun and also to clear the lines when switching to high pressure.
 

I.B. Washincars

Car Washer Emeritus
Joined
Aug 30, 2007
Messages
4,284
Reaction score
1,163
Points
113
Location
SW Indiana melon fields.
I'm with 2Biz, your's must be tee'd at the pump stand. Another thing that will delay changeovers is larger bay hoses. If you are using 3/8" you should switch to 1/4".
 

audiosnow46

Member
Joined
Feb 13, 2011
Messages
63
Reaction score
0
Points
6
Location
Rapid City, SD
yea they are T'd at the pump, and we are running 3/8". What does a manifold look like when they are T'd above the Bay or where can you get them
 

2Biz

Thread Killer!
Joined
Nov 22, 2010
Messages
2,840
Reaction score
444
Points
83
Location
Ohio
I guess its ok to post a link.....

http://www.mcmaster.com/#manifolds/=c26qht

As you can see, you can get whatever configuration and material you like. I would think Brass would be ok. SS would be more expensive, but didn't check the prices.
 

I.B. Washincars

Car Washer Emeritus
Joined
Aug 30, 2007
Messages
4,284
Reaction score
1,163
Points
113
Location
SW Indiana melon fields.
You can easily make them out of "off the shelf" brass or stainless fittings as well. I would use stainless since presoak and TC will eventually degrade brass.

I'm assuming you only have an HP line going out to your bay. You will have to extend all of your LP lines out to the top of the boom, and heres the big part, YOU MUST KEEP THEM FROM FREEZING! They will have to be wrapped with insulation or build an enclosed trough. Whoever set up this wash cheaped out by doing it the way it is now. I don't know if I've ever seen one set up that way.
 
Last edited:

mjwalsh

6 bay SS w/laundromat
Joined
Sep 7, 2007
Messages
3,134
Reaction score
173
Points
63
Location
North Dakota
More lines to protect from freezing when you do it!

You can easily make them out of "off the shelf" brass or stainless fittings as well. I would use stainless since presoak and TC will eventually degrade brass.

I'm assuming you only have an HP line going out to your bay. You will have to extend all of your LP lines out to the top of the boom, and heres the big part, YOU MUST KEEP THEM FROM FREEZING! They will have to be wrapped with insulation or build an enclosed trough. Whoever set up this wash cheaped out by doing it the way it is now. I don't know if I've ever seen one set up that way.
Nick,

As long as I.B. - Pat mentioned his insulation technique, you may want to consider the "more lines" to freeze factor in other ways also. We have weep on all our LP lines as well as the HP lines but we rarely use them because of our doors. I know Rapid City is in kind of a "banana belt" like Billings --- but it is still different than Kentucky weather wise. We definitely have our blow out system ready to use as needed --- there again --- the "more lines" means more lines have to be manifolded in the equipment room to accomplish weep & or blow out!

MJ - Mike Walsh kingkoin of Bismarck
 

Earl Weiss

Well-known member
Joined
Aug 31, 2007
Messages
6,371
Reaction score
941
Points
113
Nick,

We have weep on all our LP lines as well as the HP lines but we rarely use them because of our doors.
MJ - Mike Walsh kingkoin of Bismarck
I know you are in a cold area. But I don't think LP lInes should need to be weeped. The trough heat should take care of this. The lines should have check valves and be manifolded above the bay in the trough with check valves. Trough heat should keep them thawed to this point. The HP and FB need to be weeped because those hoses extend from the heated trough thru the same manifold into the unheated bay. That weep should keep the line open for the LP as well.
If you have a seperate LP tri foam hose that would need to be weeped and / or an anti freeze product used.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
Earl Weiss said:
I know you are in a cold area. But I don't think LP lInes should need to be weeped.
I agree. The manifolds need to be protected from freezing, but the lines themselves can expand without damage if the liquid inside freezes.
 
Top