I have lost all water through the boom on my 2.0. I replaced the Dema Valve that operates it with no luck. In manuel HP rinse mode or in a wash no HP through the boom, any ideas? Thanks!
I agree with cfcw. If you changed the valve, there is a broken signal form the card to the solenoid. Check card first. If signal is live there, then you may have a wire break. Try to find a spare wire, or run a single strand to check it.
Thanks for the help, I think you have pointed me in the right direction as the inputs appear correct and I have replaced the valve so it may very well be in the wiring. Would a voltage meter tell me if it is the wiring or is it dependent upon the command signal to register?