Motor Starter Contacts....better check!

Rudy

Active member
Joined
Sep 5, 2007
Messages
721
Reaction score
110
Points
43
Location
Pennsylvania
I was rinsing down a bay....when the pump just stopped. I went into the equipment room, and found the circuit breaker to the pump stand tripped. When I reset it....BANG! Smoke came out of the motor starter. (BTW...I hate it when the smoke comes out of electrical things....it's VERY difficult to get the smoke back in.....).

When I opened up the motor starter....the wire from the main panel was fried. About 1.5 inches of wire was obviously heating, and had finally melted, broken, and touched the metal case.

It turns out that the screw that holds this wire had loosened over the years. The loose contact caused the wire to heat...and trouble ensued.

Here's the moral to the story...

I checked the other "contacts" in the rest of the car wash motor starters. About 1/4 of them needed some degree of tightening!

You may want to check yours....... Just sayin.
 

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
792
Points
113
It is generally the simple things that get us. I used to check this even on new machines.
 

PrecisionPyro

Member
Joined
Dec 3, 2020
Messages
42
Reaction score
39
Points
18
Location
West Michigan
If you have a thermal camera for checking your floor heat, It might wise to run that over ALL of your electrical connection points over time. It can save you quite a bit of headache and money in the long run. We used to have this performed annually to all cabinets and disconnects at the Amusement Park I worked at. they paid thousands per visit, but probably saved us millions in down time.
 

Rudy

Active member
Joined
Sep 5, 2007
Messages
721
Reaction score
110
Points
43
Location
Pennsylvania
I bought a FlirOne Pro for my Android phone. It's a thermal camera attachment. It's allowed me to locate the heat loops in my floor heat.

Like everything else....it's sitting on my shelf...unused. Should of, would of could of......
 

PrecisionPyro

Member
Joined
Dec 3, 2020
Messages
42
Reaction score
39
Points
18
Location
West Michigan
Won't hurt to double check them every once in a while now though. Glad you didn't get nailed by finding it with your fingers. It's always better letting the smoke out of devices, rather than humans. (y)
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
Those screws have to be really tight. I can't tell you how many times I've gone through almost new equipment and found them so loose I could turn them by gripping the screwdriver shaft. I tighten them until I can feel the joints in my wrist pop.
 

mac

Well-known member
Joined
Sep 3, 2007
Messages
3,558
Reaction score
792
Points
113
If you have a thermal camera for checking your floor heat, It might wise to run that over ALL of your electrical connection points over time. It can save you quite a bit of headache and money in the long run. We used to have this performed annually to all cabinets and disconnects at the Amusement Park I worked at. they paid thousands per visit, but probably saved us millions in down time.
Pyro great idea. Wish I would have said that. They work and relatively cheap.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,695
Reaction score
1,438
Points
113
Location
Ohio
I just checked ours and although I definitely wouldn't call them loose they were not as tight as they should be. For some reason the ones at the top where the power comes in I could barely get them any tighter. The ones at the bottom going out to the motor I was able to tighten at least 1/4 turn and some were closer to 1/2. Good tip.
 
Last edited:

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,948
Points
113
Location
Texas
I just checked ours and although I definitely wouldn't call them loose they were not as tight as they should be. For some reason the ones at the top where the power comes in I could barely get them any tighter. The ones at the bottom going out to the motor I was able to tighten at least 1/4 turn and some were closer to 1/2. Good tip.
Did you check the ones in the middle?
 

Damoni88

Active member
Joined
Feb 23, 2019
Messages
471
Reaction score
147
Points
43
Location
Lake charles la 70605
The pump stand is constantly vibrating and these should be checked at least once a month. Make sure to turn the breaker off when checking them and re tightening.
 