What's new

Proper Gauge wire for 3 motor vacs

Scott220

Member
Joined
Nov 9, 2015
Messages
47
Reaction score
3
Points
8
Location
Maryland
Looking to upgrade from 2 motor to 3 motor vacs. Currently running approx. 80-100’ of 12 gauge wire on 20 amp breakers on the current 2 motor vacs. Any possibility of just going with 30 amp breakers and staying with 12 gauge opposed to 10 gauge? The 3 motor vacs pull 24 amps. Previous electrician said to have had a tough time pulling wire so I dread running into a problem pulling new wire if it could work.
 

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,312
Reaction score
792
Points
113
Location
Leominster, MA
Do NOT use a 30 amp breaker with 12 ga wire. You’ll have no protection at all.
Ideally, you would pull new 10ga.
what size conduit do you have? How many vacs does each conduit serve?
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,691
Reaction score
1,437
Points
113
Location
Ohio
I would suggest trying to pull new 10 gauge wire first before committing to new 3 motor vacs. Putting a 30 amp breaker on 12 gauge is against code and could cause a fire.
 

Scott220

Member
Joined
Nov 9, 2015
Messages
47
Reaction score
3
Points
8
Location
Maryland
Each vac has its own conduit. I’ll have to check size of conduit. Appreciate your input!
 

I.B. Washincars

Car Washer Emeritus
Joined
Aug 30, 2007
Messages
4,289
Reaction score
1,171
Points
113
Location
SW Indiana melon fields.
Jim Gosnell told me several years ago that he devised something for this scenario. IIRC, two of the motors start and get up to speed, shut off momentarily as the third starts, then restarts the others while they are coasting, keeping the amp draw at less than 20A. I'm thinking all of this happens within a second or so.
 
Last edited:

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,691
Reaction score
1,437
Points
113
Location
Ohio
Jim Gosnell told me several years ago that he devised something for this scenario. IIRC, two of the motors start and get up to speed, shut off momentarily as the third starts, then restarts the others while they are coasting, keeping the amp draw at less than 20A. I'm thinking all of this happens within a second or so. I
We have a JE Adams vac that does something similar but starts just one at first and then the second and then the third if turbo is selected.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,691
Reaction score
1,437
Points
113
Location
Ohio
Can it do that using #12 wire?

I think it just keeps the start up amp spike down. It is on a 25 Amp breaker and has never tripped. I'll check the amp draw with a clamp on meter if I can remember to do it.
 

tdlconceptsllc

Well-known member
Joined
Jul 30, 2013
Messages
1,065
Reaction score
431
Points
83
Location
NC
Remember also a High leg site will pull less amps also like a true 230 site vs a 208v site. I had to cut the parking up at my wash to instail 10 gauge wire it sucks older washes always have 12
 

wash4me

Member
Joined
May 15, 2012
Messages
481
Reaction score
3
Points
18
Location
Kansas City
I agree with others it is wrong to put a 12 gauge wire on a 30 amp breaker. That being said it will work and you do still have some protection on the wire. Unlikely to cause a problem.
 

cmawash

Member
Joined
Jun 7, 2013
Messages
176
Reaction score
16
Points
18
Location
camarillo calif.
JUST FINISHED UPGRADING WIRE TO 8 GAGE HAD SOME 12 AND 10 GAGE, LUCKELY THE CONDUIT WAS BIG ENOUGH , GOT RIDE OF A LOT OF SPICES, SUB GAGE WIRING AND UPGRADED GROUNDING. EQUIPMENT OPERATION WAS NOTICEABLE
 
Top