2Biz: Also since these are condensing uinits, are the coils stainless steel or aluminum?
Bubbles Galore:
My documentation stated that they were stainless
I copied this information from a Takagi T-M32 ASME Document I found online...Looks like the coils are copper. The burner is S.S. After reading the manual for the T-M32, the condensation is controlled by a "Vertical Condensation Drain" installed just above the unit in the flue pipe.
http://www.kleen-ritecorp.com/p-21258-4-universal-condensate-drain.aspx
Mobius water heater(s) shall be Model T-M32 ASME as manufactured by Takagi Industrial Company, Inc. The Mobius water heater(s) shall be a copper coil integral fin and tube construction with quick release brass or bronze waterways. Heater(s) will be factory assembled and tested.
The heater shall be vented with 4” Stainless steel Category III vent pipe a distance not to exceed 50’ (equivalent) feet terminating vertically or horizontially as prescribed. Intake air with optional direct vent kit may be of such material as PVC not to exceed a total of 50’ (equivalent).
The heater(s) shall be controlled by onboard solid state printed circuit board monitoring incoming and outgoing temperatures with factory installed thermistors, sensing and controlling flow rate to set point temperature with control both air and gas mixture inputs to maintain thermal combustion efficiency. Unit also consists of ground fault interrupter, inline fusing, spark ignition and sensor system, aluminized stainless steel burners, air-fuel ration rod, Hi limit switch, modulating and proportional gas valves, freeze protection sensor and heating block and overhead cut-off fuses.
The water heater(s) shall be CSA listed, exceeds the energy efficiency requirements of ASHRAE 90. 1b-1992.