I currently have a 5 gal water heater circulating antifreeze through the automatic wash rails and the trough for half of my 4 bay wash. I want to tee in and add lines to the other half of my wash. Is this water heater enough to tackle the extra runs of 3/4" trough heat??
 

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,131
Reaction score
585
Points
113
Location
CO
Probably. But, what's the DeltaT on the current configuration?
 

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,131
Reaction score
585
Points
113
Location
CO
Temperature difference of the heater's outlet and inlet = deltaT

Assuming, 120' of 3/4 PEX for the additional 4 bay trough...that adds less than 2 gallons of glycol to the system. And, since the trough is likely insulated, the temperature drop through the new section won't be as significant. (No where near the exposed rail section.)
 

Edie011

Member
Joined
Feb 18, 2014
Messages
64
Reaction score
0
Points
6
Location
Strasburg, ohio
Temperature difference of the heater's outlet and inlet = deltaT

Assuming, 120' of 3/4 PEX for the additional 4 bay trough...that adds less than 2 gallons of glycol to the system. And, since the trough is likely insulated, the temperature drop through the new section won't be as significant. (No where near the exposed rail section.)
What is a good way to add a tee for the new lines and a spot to add antifreeze?
 

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,131
Reaction score
585
Points
113
Location
CO
Dultmeier's got a pretty good diagram here:
https://www.dultmeier.com/prod-info.php?info=huMM-P306N-Heating-System.jpg
 