This thread has got me thinking. I wonder if I've been running my unit at less than an "efficient" mode.

I had a 1 membrane Applied Membranes unit that was expanded to 2 membranes decades ago (when I added an additional automatic bay). The motor/pump was also up-sized.

I've been running the Product and Reject flows equally.

If I understand things....this is a 50% recovery rate....Correct?

Per my earlier post, I'm now running XLE (Extra Low Engery) membranes at 100psi.

Today, I readjusted the flow settings to achieve a 4.0 gpm Product and a 1.5 gpm Reject flowrate. The recirculation flow is 2.5 gpm.

Am I doing the math correctly and I now have a 73% recovery rate? (4.0 divided by 5.5)

And.....this rate is OK?

It sure saves dumping water down the drain if true............
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,653
Reaction score
1,413
Points
113
Location
Ohio
This thread has got me thinking. I wonder if I've been running my unit at less than an "efficient" mode.

I had a 1 membrane Applied Membranes unit that was expanded to 2 membranes decades ago (when I added an additional automatic bay). The motor/pump was also up-sized.

I've been running the Product and Reject flows equally.

If I understand things....this is a 50% recovery rate....Correct?

Per my earlier post, I'm now running XLE (Extra Low Engery) membranes at 100psi.

Today, I readjusted the flow settings to achieve a 4.0 gpm Product and a 1.5 gpm Reject flowrate. The recirculation flow is 2.5 gpm.

Am I doing the math correctly and I now have a 73% recovery rate? (4.0 divided by 5.5)

And.....this rate is OK?

It sure saves dumping water down the drain if true............

I was told by several others year ago that I should run close to a 1:1 but favoring just a tad bit more on the reject water. With the reject all the way cranked down I can just barely get a little more product water than reject. Maybe it's designed that way?
 

HeyVern

Well-known member
Joined
Jun 27, 2021
Messages
404
Reaction score
467
Points
63
This thread has got me thinking. I wonder if I've been running my unit at less than an "efficient" mode.

I had a 1 membrane Applied Membranes unit that was expanded to 2 membranes decades ago (when I added an additional automatic bay). The motor/pump was also up-sized.

I've been running the Product and Reject flows equally.

If I understand things....this is a 50% recovery rate....Correct?

Per my earlier post, I'm now running XLE (Extra Low Engery) membranes at 100psi.

Today, I readjusted the flow settings to achieve a 4.0 gpm Product and a 1.5 gpm Reject flowrate. The recirculation flow is 2.5 gpm.

Am I doing the math correctly and I now have a 73% recovery rate? (4.0 divided by 5.5)

And.....this rate is OK?

It sure saves dumping water down the drain if true............
When mine was installed they told me it is best to keep the product and reject equal. You can turn the reject down but that will shorten the life of the membranes.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,653
Reaction score
1,413
Points
113
Location
Ohio
I turned it back on today and the best I can get now is 3.3 GPM product and 3.4 reject. The pressure regulator appears to be seized inside. I can crank the screw all the way in or out and doesn't seem to change the pressure. Right now it's about 180 psi. The tag on the pump says 250 psi max and 16 GPM. The regulator is a US Para Plate 13064 but can't find one on the innerwebs. The closest I found is one at KR but has a high pressure range.

https://www.kleen-ritecorp.com/p-17...d-back-pressure-regulator-1000-psi-8-gpm.aspx
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,653
Reaction score
1,413
Points
113
Location
Ohio
Also I forgot to mention that it's putting out 1 PPM TDS now. 264 PPM input and 530 PPM reject.
 

Dan kamsickas

GinSan Technician
Joined
Aug 31, 2007
Messages
705
Reaction score
942
Points
93
Location
Grand Rapids, MI
What is the GPM of the pump? Typically the pump is a 10GPM for two membranes with a 7gpm flow control on the output.
 

Rudy

Active member
Joined
Sep 5, 2007
Messages
717
Reaction score
106
Points
43
Location
Pennsylvania
I have a 8GPM Procon run by a 1.5 HP Baldor motor in my 2 Membrane setup.
 

Rudy

Active member
Joined
Sep 5, 2007
Messages
717
Reaction score
106
Points
43
Location
Pennsylvania
I still a little confused.

Is it best to run a 1:1 product:reject rate (50% recovery), or is it OK to turn up the recirculation and have a 75% (or higher) recovery rate?
 

HeyVern

Well-known member
Joined
Jun 27, 2021
Messages
404
Reaction score
467
Points
63
I still a little confused.

Is it best to run a 1:1 product:reject rate (50% recovery), or is it OK to turn up the recirculation and have a 75% (or higher) recovery rate?
Ideal is 1:1 you can turn up the recirculation but it will shorten the life of your membranes
 

Buckeye Hydro

Active member
Joined
Jun 18, 2022
Messages
198
Reaction score
128
Points
43
The ratio of permeate to concentrate is affected in a big way by the quality of your feedwater. Let's start there. Is your feedwater less than 1 gpg hardness?
 

Buckeye Hydro

Active member
Joined
Jun 18, 2022
Messages
198
Reaction score
128
Points
43
Minimum recommended concentrate flow on a 4" diameter membrane or series of 4" membranes is 3 gpm.
 

Buckeye Hydro

Active member
Joined
Jun 18, 2022
Messages
198
Reaction score
128
Points
43
Assuming you have them plumbed in series, go no lower than 3 gpm on the concentrate, and if you're at membrane spec pressure and temperature, you should be at about 2500x3=7500/1440=5.2 gpm permeate. adjust this equation if the membranes aren't 2500 gpd, and for your pressure and temperature.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,653
Reaction score
1,413
Points
113
Location
Ohio

Rudy

Active member
Joined
Sep 5, 2007
Messages
717
Reaction score
106
Points
43
Location
Pennsylvania
Ideal is 1:1 you can turn up the recirculation but it will shorten the life of your membranes
The cost of water, and more so, the sewer....is very high in my location. At some point, it's cheaper to accept the lower life of the membranes in exchange for lower operating costs. The question, is where to draw that line.

The ratio of permeate to concentrate is affected in a big way by the quality of your feedwater. Let's start there. Is your feedwater less than 1 gpg hardness?
Yes, the quality of the water here is excellent. The feedwater has 0 grains of hardness after the softeners (and it's tested daily).
 