I hope someone can help
I have a SS bay using 8 pos double stack switch with dixmor timer. I have HP soap, wax and rinse when on HP soap or wax I get a voltage drop to 16 or 17 volts however on the rinse positions everything operates normally. the voltage drop causes the relay to chatter and eventually burn out. Any ideas where i can start for problem solving. I put in a new rotary switch swapped timers put in new transformer no help.
Thanks
Jaye
 

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,297
Reaction score
753
Points
113
Location
Leominster, MA
Is there a solenoid that both the soap and wax use but the rinse doesn’t? For example, they open a hot water solenoid but the rinse is cold.
What brand of equipment is this?
 

Jaye

New member
Joined
Aug 12, 2009
Messages
8
Reaction score
0
Points
1
Location
georgia
there is a separate solenoid for the soap and the wax no cold water valve
 

Jaye

New member
Joined
Aug 12, 2009
Messages
8
Reaction score
0
Points
1
Location
georgia
my thinking is there is contact between the wax and soap valve activation wires but I checked wires individually and they ring out good
 

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,297
Reaction score
753
Points
113
Location
Leominster, MA
my thinking is there is contact between the wax and soap valve activation wires but I checked wires individually and they ring out good
I’d think that would cause a dead short. I think there is another solenoid, relay etc that both functions share.
Are all of your HP functions cold water, all hot or mixed?
 

Jaye

New member
Joined
Aug 12, 2009
Messages
8
Reaction score
0
Points
1
Location
georgia
I’d think that would cause a dead short. I think there is another solenoid, relay etc that both functions share.
Are all of your HP functions cold water, all hot or mixed?
all functions cold water
 

Jaye

New member
Joined
Aug 12, 2009
Messages
8
Reaction score
0
Points
1
Location
georgia
I have a solenoid that rinse wax and soap share in the bay box though i dont understand the purpose since its 24v activating a 24v conection
 

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,297
Reaction score
753
Points
113
Location
Leominster, MA
it’s time to start the process of elimination. Double check that all conductors are free of corrosion and have good contact at the terminal blocks. Then, disconnect the soap solenoid and check voltage drop, then do the same for wax solenoid, motor contactor etc. You’ll find it eventually
 

Jaye

New member
Joined
Aug 12, 2009
Messages
8
Reaction score
0
Points
1
Location
georgia
thats why I have been shotgunning parts I'm still looking just getting frustrating
 

cmawash

Member
Joined
Jun 7, 2013
Messages
171
Reaction score
16
Points
18
Location
camarillo calif.
TO START TROUBLE SHOOTING what the size of the transformer ( how many VA). is the problem one bay or all bays.
 

Randy

Well-known member
Joined
Sep 5, 2007
Messages
5,858
Reaction score
2,208
Points
113
I'll bet you've got a bad soleniod. Start by disconnecting each soleniod and check for the voltage drop as you disconnect the solenoids.
 
Top