I work for a heating company. Just left a car wash that has two wands at the entrance for pre soaking. The wands provide a soap and water mixture. Another company removed a boiler that heated this mixture and installed a on demand water heater that will not maintain hot water to the mixture. I am looking for help to restore this setup back to the correct working order. Thanks!
 

Eric H

Well-known member
Joined
Aug 30, 2007
Messages
1,297
Reaction score
753
Points
113
Location
Leominster, MA
The tankless unit probably has enough BTU's to get the job done. I suspect the unit is cycling on and off constantly if it is feeding the guns directly. You're getting a cold water sandwich that brings the desired temp down.
You can use a 30 gallon storage tank and have the tankless unit feed the storage tank using a circulator pump and t-stat. Then take a line from another port on the storage tank to feed the pumps.
I use this setup to feed 2 self serve bays and 2 IBA's with a single Rainni, i don't remember the BTU's but it isn't very big.
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,653
Reaction score
1,413
Points
113
Location
Ohio
I work for a heating company. Just left a car wash that has two wands at the entrance for pre soaking. The wands provide a soap and water mixture. Another company removed a boiler that heated this mixture and installed a on demand water heater that will not maintain hot water to the mixture. I am looking for help to restore this setup back to the correct working order. Thanks!

How many BTUs does the new unit have and what is the GPM output combined on the two wands? How is the soap fed in?
 

Shayne

New member
Joined
Oct 17, 2022
Messages
2
Reaction score
0
Points
1
I work for a heating company. Just left a car wash that has two wands at the entrance for pre soaking. The wands provide a soap and water mixture. Another company removed a boiler that heated this mixture and installed a on demand water heater that will not maintain hot water to the mixture. I am looking for help to restore this setup back to the correct working order. Thanks!
The tankless unit probably has enough BTU's to get the job done. I suspect the unit is cycling on and off constantly if it is feeding the guns directly. You're getting a cold water sandwich that brings the desired temp down.
You can use a 30 gallon storage tank and have the tankless unit feed the storage tank using a circulator pump and t-stat. Then take a line from another port on the storage tank to feed the pumps.
I use this setup to feed 2 self serve bays and 2 IBA's with a single Rainni, i don't remember the BTU's but it isn't very big.
The tankless unit probably has enough BTU's to get the job done. I suspect the unit is cycling on and off constantly if it is feeding the guns directly. You're getting a cold water sandwich that brings the desired temp down.
You can use a 30 gallon storage tank and have the tankless unit feed the storage tank using a circulator pump and t-stat. Then take a line from another port on the storage tank to feed the pumps.
I use this setup to feed 2 self serve bays and 2 IBA's with a single Rainni, i don't remember the BTU's but it isn't very big.
Thank You for your help!
 