I am adding another iba to my wash. There is a possibility that my incoming water service is under sized. Have any of you added additional water storage to help out? Storage tank, booster pump, bladder tank...how did you do it?
 

robert roman

Bob Roman
Joined
Sep 11, 2007
Messages
2,200
Reaction score
3
Points
36
Location
Clearwater, Florida
When developing a new carwash or renovating an old wash, investors plan for great success not mediocrity.

If you’ve made the financial commitment to add innovation (new IBA), why saddle it with mediocre infrastructure – possibility of an inadequate water supply.

Not only does this create possibility of operations risk from insufficient sales it also creates the possibility of re-sale market risk as in fair value.

The best way to mitigate these risks is to plan for a reliable water supply (i.e. increase size of water main).
 

Washmee

Fullservice Tunnel
Joined
Sep 3, 2007
Messages
973
Reaction score
2
Points
18
Location
Canton, Ohio
When developing a new carwash or renovating an old wash, investors plan for great success not mediocrity.

If you’ve made the financial commitment to add innovation (new IBA), why saddle it with mediocre infrastructure – possibility of an inadequate water supply.

Not only does this create possibility of operations risk from insufficient sales it also creates the possibility of re-sale market risk as in fair value.

The best way to mitigate these risks is to plan for a reliable water supply (i.e. increase size of water main).
You realize that sometimes that's just not possible. I had a similar problem after I bought my wash. There was not enough supply or pressure and the city water utility said too bad, they had no intention of doing anything about the problem. My wash was built in 1956 and over the years many other businesses were built and supplied by the same 4 inch main that supplied the wash. On certain days and times my water pressure would drop as low as 15psi coming into the building. I added a booster pump and several bladder tanks to help stabilize the flow and pressure. My final solution was to drill a well for wash water use only.
 

Waxman

Super Moderator
Joined
Aug 31, 2007
Messages
6,051
Reaction score
1,697
Points
113
Location
Orange, MA
In my IBA I store my RO reject and use it in the IBA.

You could do the same thing; I use a 250 gal tote and pump it into my IBA feed tank via a Little Giant pump w/dual float setup.
 

robert roman

Bob Roman
Joined
Sep 11, 2007
Messages
2,200
Reaction score
3
Points
36
Location
Clearwater, Florida
You realize the situation you described is a rare exception rather than the norm.

What municipality would allow water main pressure to drop below minimum standards without being due to external factors like drought, sinkhole, etc.?

I never heard of such a thing. How did the new guys obtain permits?
 

Jeff_L

Well-known member
Joined
Dec 27, 2007
Messages
1,246
Reaction score
31
Points
48
Location
Missouri
Ric - I do something similar to Waxman. My RO reject goes upstairs to about 6-7 55gal drums all laying on their side and plumbed together with 2" PVC pipe. Since they are upstairs, they gravity feed into my two IBA's. I also have a 30gal drum right-side up plumbed into them that has a float that opens the valve to the city feed in case the tanks go low from a lot of use and not enough time between cars for the RO to regenerate enough. This, however, doesn't solve your hot water input, unless you plumb RO reject to both a holding tank and to a water heater.
 

Washmee

Fullservice Tunnel
Joined
Sep 3, 2007
Messages
973
Reaction score
2
Points
18
Location
Canton, Ohio
You realize the situation you described is a rare exception rather than the norm.

What municipality would allow water main pressure to drop below minimum standards without being due to external factors like drought, sinkhole, etc.?

I never heard of such a thing. How did the new guys obtain permits?
I don't know, maybe you could ask them or the water utility. The wash wash built in 1956 and I would guess that at the time the line was big enough. The average water pressure is only 40psi to begin with.
 

ToFarGone

Member
Joined
Feb 18, 2012
Messages
67
Reaction score
1
Points
6
Location
Burlington Iowa
You realize the situation you described is a rare exception rather than the norm.

What municipality would allow water main pressure to drop below minimum standards without being due to external factors like drought, sinkhole, etc.?

I never heard of such a thing. How did the new guys obtain permits?
If you build on the south end of my city you will be told to install boosters. It has been this way for years.
 

Ric

Cantree Member
Joined
Aug 31, 2007
Messages
967
Reaction score
5
Points
18
Location
West Michigan
In my IBA I store my RO reject and use it in the IBA.

You could do the same thing; I use a 250 gal tote and pump it into my IBA feed tank via a Little Giant pump w/dual float setup.
What are you using for a float setup? Electrical, in order to tell the pump to turn on?
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
A pump controlled by a VFD and a pressure transducer can maintain pressure without large storage tanks, and it's more efficient since the pump only runs as much as needed.
 

Washmee

Fullservice Tunnel
Joined
Sep 3, 2007
Messages
973
Reaction score
2
Points
18
Location
Canton, Ohio
A pump controlled by a VFD and a pressure transducer can maintain pressure without large storage tanks, and it's more efficient since the pump only runs as much as needed.
Thats how my water well is set up. Very efficient and makes the pump last longer.
 

pgrzes

Active member
Joined
Oct 21, 2007
Messages
878
Reaction score
32
Points
28
Location
S.E. Pa.
I have reject going into tanks in the attic and just gravity feed into my auto's tank. I have a Jobe float valve on 1- 3/4" line and an overflow that just drains into the autos tank. I also have my reclaim going into attic tank for Undercarriage blast.
 

wash4me

Member
Joined
May 15, 2012
Messages
481
Reaction score
3
Points
18
Location
Kansas City
A pump controlled by a VFD and a pressure transducer can maintain pressure without large storage tanks, and it's more efficient since the pump only runs as much as needed.
This sounds like a good idea. I would think that you could also install some sensors and have it where the pressure had to be low and the float tanks also had to be below a certain level before the pump came on. When the wash isn't busy even with low pressure the tank could recover.
 

MEP001

Well-known member
Joined
Aug 30, 2007
Messages
16,665
Reaction score
3,946
Points
113
Location
Texas
That might be ok as long as there are no Hydrominders relying on consistent pressure.
 