I've got a Fleck 2750 valve on a 14"x65" tank. When more than 3 SS bays are running the carwash is starved for water and all the pumps go dry. After some investigation, I determined that the softener was restricting the flow. I've got it bypassed so at least I can run. I don't know where or how to start to look where the restricion is. Would it be in the valve or resin bed? Best I can figure, that softener should flow about 40 gpm with a 15 psi pressure drop. I am flowing about 10-15 gpm with a 50 psi pressure drop. Any help?