Another thought. A couple of years ago I had to replace the motor contactor on an air compressor. It worked fine for a day or two, then stopped working. I discovered that the coil was bad on the new contactor. The electric supply house gave me a new one. A couple of days later, same thing. They gave me another one. Once again, same thing a couple days later. As Jethro Bodine would do, I got to doing some ciphering. I soon noticed that I was using 120V coils on the contactor that was wired 208. Since it was only about 6" from the electric panel, I just ran a neutral wire and used what I already had instead of driving 1/2 hr back to the supply house. I also didn't have to go tell them that I was a dumba$$.