You gotta determine the color of the wire at your wash as MEP suggested. Ideally the wire color connected to the solenoid is the same one out in the bay. To check in the bay, get a multimeter and read voltage off the back of the switch. The first step is to identify the wire colors coming in that provide 24V, neutral, and ground to the meter. These are usually black, white ,and green. You also need to identify the timed output which comes out of the timer and connects to the rotary switch. When energized, the timed output of your timer will energize the rotary switch at position 0, which will be numbered as 10 and 20. The switch acts as a gate to allow energy to flow back to the equipment room and energize the necessary outputs.
Once you have these identified the 24V, common, ground, and timed output, start the meter and turn the switch to the first function. Then read which wire now has voltage on it. You'll probably find that is the one that is 180 degrees opposite from the flat spot on the switch post (you can see the flat spot if you remove the knob.. Lets' says it's purple. Write it down. then find what color wires are energized on the other functions: foam brush, SFR,etc. High pressure functions require a separate isolated output on the second ring of contacts to energize the pump motor. This second ring usually has a wire harness with several wires connected together. So, high pressure
soap may require position 14 AND 24, Rinse may require 15 and 25, wax 17 and 27, etc
If you don't know electrical, you may likely just identify different color wires and see which switch number they are hooked up on in other bays.
I have seen on rare occasions where wires have been spliced and (God forbid) even colors changed in junction boxes. But if a rational person built and serviced this wash, all bay wiring should correspond with each other.
Guys, does this make sense?