I'm considering using an additional temperature controller instead of the Weep Mizer's output 2 because it looks like it has only a 1 degree differential. Correct me if I'm wrong.
Why....When it gets cold out, temp is coming down and usually goes past setpoint....Slabs already warmer from the higher temps of the day. I control my floor heat pumps from output 2...Never have seen it short cycle...I have output 2 set at 32°....Using a different controller and The larger diffferential you set will keep it on longer than necessary that wastes energy. If the temp is rising, why would you want it staying on at 33° or more after the slabs are already warm? I'm sure you are already aware, but you need to make sure you have a relay big enough to handle the load of all your pumps. Use output 2 to control that relay...I'm sure the bayite controller will work though. I have several of them controlling various things...
Coin Box heaters, Pop machine heaters, Attic fan ventilators at home, etc....They are a great little temp controllers that doesn't break the bank @ $20 each!...