Take a shovel and cover the hole area with a light dusting of snow...IF your able to run the boiler then look for the melting spot.

If your able to shut off zones you can shut all down and open one at a time with air pressure in the lines
 

dogwasher

Member
Joined
Sep 8, 2007
Messages
398
Reaction score
0
Points
16
Worst case there are companys with xray cameras(they charge $ for this) and they can see the hot spot threw the concrete
 

Buzzie8

Member
Joined
Dec 12, 2007
Messages
942
Reaction score
2
Points
16
Location
Pittsburgh, PA
A local firemen I know came up to my wash at night with their infrared camera. It gives decent images but not perfect. Most local fire companies have these cameras now.
 

DiamondWash

Well-known member
Joined
Aug 31, 2007
Messages
2,373
Reaction score
478
Points
83
Location
Des Moines, Iowa
We just got our floor heat back up and operational with 3/4 of the loops working after finding a leak we just shut off the loops that we think are the problem until summer time when we can tear up concrete and repair them it turns out that the pex tubing was ran too far in our exit and they made a cut line in the concrete above it then this winter the concrete heaved and snapped/pinched the pex $$$$
 

mjwalsh

6 bay SS w/laundromat
Joined
Sep 7, 2007
Messages
3,134
Reaction score
173
Points
63
Location
North Dakota
We just got our floor heat back up and operational with 3/4 of the loops working after finding a leak we just shut off the loops that we think are the problem until summer time when we can tear up concrete and repair them it turns out that the pex tubing was ran too far in our exit and they made a cut line in the concrete above it then this winter the concrete heaved and snapped/pinched the pex $$$$
Ric, Diamond, & others,

This might not be for everyone but I actually used R7 braided hi pressure hydraulic hose with the smallest bend radius that I could find for part of our deicer add on section & even a floor heat section. I got the idea from when I allowed a contractor with a local wholesaler use what seemed to be a lot less tough hose in a contract situation ---- I don't think either specific hose is made anymore nowadays but there could be others with the suitable bend radius etc. Time will tell if --- it was the best decision. I figure if it keeps pace with heating requirement --- the heat efficiency should not be different --- I could be wrong.