I am considering ripping out my concrete and putting in new floor heat at one location. I'm confused about what depth concrete I need to get quoted. I think the floor heat loops sit about 2" under the surface, but I'm told I need 6-8" of concrete. How would that work, and how deep would I actually need to remove from the old and pour new?
 

cantbreak80

Maybe I need new clubs
Joined
Feb 10, 2008
Messages
1,131
Reaction score
585
Points
113
Location
CO
We’ve always spec 4” of 4000+ psi concrete on compacted base.
We install 1/2” O2 barrier PEX over 3” foam insulation (Crete-Heat). The contractor must lower the finished grade to accommodate the new finished floor elevation.
IMG_1461.jpg


Side note:
Concrete must have been really cheap in the late 70’s. This tear-out revealed upwards of 10” of concrete with black poly pipe directly on the dirt.
No wonder there were multiple cold spots.
IMG_0248.JPG IMG_0252.JPG
 

OurTown

Well-known member
Joined
Nov 8, 2017
Messages
3,691
Reaction score
1,437
Points
113
Location
Ohio
We’ve always spec 4” of 4000+ psi concrete on compacted base.
We install 1/2” O2 barrier PEX over 3” foam insulation (Crete-Heat). The contractor must lower the finished grade to accommodate the new finished floor elevation.
View attachment 9431


Side note:
Concrete must have been really cheap in the late 70’s. This tear-out revealed upwards of 10” of concrete with black poly pipe directly on the dirt.
No wonder there were multiple cold spots.
View attachment 9432 View attachment 9433

Have you ever replaced the floor on a wash with a monolithic slab foundation?
 

slash007

Well-known member
Joined
Jul 8, 2012
Messages
2,479
Reaction score
417
Points
83
Location
Lexington, Ky.
We’ve always spec 4” of 4000+ psi concrete on compacted base.
We install 1/2” O2 barrier PEX over 3” foam insulation (Crete-Heat). The contractor must lower the finished grade to accommodate the new finished floor elevation.
View attachment 9431


Side note:
Concrete must have been really cheap in the late 70’s. This tear-out revealed upwards of 10” of concrete with black poly pipe directly on the dirt.
No wonder there were multiple cold spots.
View attachment 9432 View attachment 9433
So you are pouring 4" of concrete on top of the foam insulation? Not sure what you mean exactly by "lower the finished grade to accommodate to the new finished floor elevation"?
 

HeyVern

Well-known member
Joined
Jun 27, 2021
Messages
410
Reaction score
475
Points
63
So you are pouring 4" of concrete on top of the foam insulation? Not sure what you mean exactly by "lower the finished grade to accommodate to the new finished floor elevation"?
The dirt has to be 4" lower to accommodate the extra 4" of insulation so that the finished floor isn't 4" too high.
 