*****Posted For cantbreak80*****
Attached is my 3 bay air blow out program…
Without modification, each bay will blow out twice for 10 seconds with 30 second intervals.
First blow out is controlled by thermostat set point…delay is 5 seconds for simulation purposes. Change that to 5 minutes in the operational program.
IF a bay is in use during the initial blowout, it’s blowout will occur after the switch state is off.
A 2 second delay prevents excessive operation.
The blowouts occur 30 seconds after the customer switches off the selection...giving the customer a chance to step away from the application device.
To increase blowout times, change the Pulse Generator ON times from 10 to 15 seconds and adjust the Cycle Timers to 90 seconds.
To make the system blow out 3 times, adjust the cycle timers to 3 times the total Pulse Generator time.
cantbreak80 (Larry)
Program can be downloaded here:
http://www.bcoweb.com/photos/ABO_v3.3.lsc
This program is more complex than mine and Larry thought of something I didn't, actually a lot more that I didn't think of. He added a (Much Needed) blowdown when the thermostat kicks on. Up to this point, my program doesn't have this. With my program, if a bay didn't get used after the thermostat kicked in, the bay could freeze.
Very well done Larry, Thanks for sharing!